SRT battery replacement will not update
Hi all.
My client has replaced batteries, but the battery replacement date for the internal and external batteries will not update.
The units are SRT3000XLI manufactured 2015/2019.
Both has the same issue.
configuration->Battery->internal date-> change date (All RBC)
I there any specific procedure other than the above. Does the unit require a firmware upgrade
Please see media attached
- Labels:
-
Home & Office - UPS & Software
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-13 04:41 AM
Configuration -> UPS -> Last Battery Replacement: Enter Month / Year and Apply.
Reboot the UPS, Initiate a manual Self Test than complete a Battery Calibration as outlined above.
Please let me know if you have more questions. If not and this information resolved the issues ensure you mark this as solved. 👍
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-07 07:17 AM . Last Modified: 2024-05-07 07:18 AM
Starting with the main UPS disconnect the battery cartridge and wait for the unit to declare a fault. Wait another 30 seconds and reconnect the cartridge.
The system should prompt you to confirm this is a (New) battery cartridge select YES and enter the month and year than OK / Save.
Confirm the new month and date is present on the (Main) UPS! ☝️
If it is you can do the same for the extended battery packs. You must wait for the system to declare a fault (missing battery) than wait 30-60 seconds before reconnecting the battery terminals.
This is a lot easier via the NMC if present. 👍
Once the battery dates have been updated reboot the UPS. Next, complete a Self Test of the system. Lastly initiate a battery calibration to insure the system knows the correct operational runtime.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-12 11:50 PM
Appreciate your assistance, how do you update using the NMC, AP9630 installed at the moment.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-13 04:41 AM
Configuration -> UPS -> Last Battery Replacement: Enter Month / Year and Apply.
Reboot the UPS, Initiate a manual Self Test than complete a Battery Calibration as outlined above.
Please let me know if you have more questions. If not and this information resolved the issues ensure you mark this as solved. 👍
Link copied. Please paste this link to share this article on your social media post.