Problem with UPS ES 700G

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Problem with UPS ES 700G
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
7
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

Problem with UPS ES 700G

I have this UPS for 2 years now and I did not have any problem until now.

Every once in a while the UPS seems to "cut" the electricity of the equipment that is conncted to it momentarily since all the equipemnt restart.

I have connected two nas, one switch and on adsl modem. When I log on to the devices it sees that were restarted forcefully like someone turned them from the plug.

Can someone explain why this is happening and how can I troubleshoot this kind of problem?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-27 02:17 AM

I left the UPS unplugged for over  30 hours with minimal load so that the battery will go to 1%.

Then I try to charge it again but after 8 hours it stayed at 1%.

I followed the procedure that Jordan recommended but unfortunately after I tried to charge again the UPS again stayed at 1%.

I do not have either another UPS  or another battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

Nicolas,

Could you provide the exact model and serial number of the unit as it appears on the white sticker on the back of it?  During these "cuts", is there any issue with utility power in your building?  Do you have any data and event logs you can provide from the unit? Has there ever been any fault indicators on the unit?  Aside from these "cuts", if you were to similuate a power outtage, (for example, pull the plug of the UPS to see if goes to battery as it should... Note: I would not try this during business hours but wait for downtime to test) would it go to battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

Hi Jordan.

The exact model number is BE-700G Uk serial number is 5B1335T05787.

The powerchute shows estimated battery time 42min and no alert or what so ever. 

When I simulate the power outtage you were right, the devices are all shuwdown, i.e. the UPS does not stay switch to batteries.

What does this mean? Can I do something about this?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

Hi,

Does the UPS keep the systems running for any amount of time or do they crash as soon as AC is cut? If they crash immediately and the UPS is displaying 42 minutes of run time it sounds like the systems are plugged into the surge only outlets and not the battery surge outlets. If they are plugged into the proper outlets I suggest testing to see if the UPS will sustain a load using a lamp. Power down and unplug all the attached systems. Plug a lamp into one of the battery outlets and then remove AC from the UPS. If the lamp stays on then the UPS is working properly.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

They crash immediately as soon as AC is cut. No the plugs are in the battery surge outlets, they jsed to work just perfect.

I did a test with a lamp and I am getting the exact same behavior. It doe snot matter is I have 1 device or 5.  When AC goes off everything on the UPS goes off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-27 02:17 AM

Hi Nicolas,

I would recommend calling into your local support and inquiring about the warranty status of this backups. It sounds like either the battery or the UPS needs to be replaced.

If you have another UPS of this same type, you could swap the battery and repeat the test to verify it's a battery issue (and relay that to the local support). I'm leaning towards a battery related problem, but it's odd the software is indicating a high runtime. You mentioned in your first post, this issue happens every once in a while. I wonder if it's every two weeks when the UPS runs a self test (which puts the UPS on battery). Other info I would be curious about - is there any reason the battery would have issues this soon that you can think of (such as frequent power issues, heat, etc.)?

Let us know if we can help further.

Thanks,

Tommy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-27 02:17 AM

I would recommend running a brain dead procedure:

1) Turn of the unit

2) Unplug the unit from the wall

3) Unplug the equipment attached to the unit

4) Remove the internal battery

5) Hold down the power button for about 20 seconds

6) Reconnect everything and power up the unit

At this point, check for any changes, including re-running the test mentioned above.  If no changes, I would suggest contacting your local support for further assistance.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
1218
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-27 02:17 AM

I left the UPS unplugged for over  30 hours with minimal load so that the battery will go to 1%.

Then I try to charge it again but after 8 hours it stayed at 1%.

I followed the procedure that Jordan recommended but unfortunately after I tried to charge again the UPS again stayed at 1%.

I do not have either another UPS  or another battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore