F04 - Clamp Short error occurs frequently

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • F04 - Clamp Short error occurs frequently
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
2
13281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:18 AM

F04 - Clamp Short error occurs frequently

i searched the forum but couldnt find anything useful. firstly reading through the forum i understand what clamp short might mean but i`m struggling to decide if i should return my UPS or try to find the fault if possible and fix that.

i purchased this UPS on the 12th of june 2005 and its been working very nicely for 2 days. the 3rd day (15th June) when i came home there was a power surge and the UPS was making a weird continous low pitch noise with an error code F04. reading through this forum i found out that i should unplug everything - remove the battery and leave for 5 minutes - plug back in and it all works well as mentioned here.

problem is now its frequent and its happened for the 6th time today. being in a country like srilanka we really have abosoulty horrible grid power so a UPS is essential. could it be that the UPS is faulty ? what steps can i take to test this out before going to return this ?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 1500gi
  • clamp
  • f04
  • short
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
13276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:18 AM

help please..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
13276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:17 AM

Hi,

If you need urgent support at anytime, I'd recommend you contact your local support office for the quickest response.

Can you let me know what model of UPS this is? I am looking for the model number on the white sticker on the back or bottom. It sounds like a BR or BX something but it may be a region specific model where F04 is triggered by a certain threshold or something that is different from other units.

From the general information I've found, it appears if it continues that the unit may need to be replaced but depending on what is causing it, the root problem may damage any new or replacement UPS too.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
13277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:18 AM

help please..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:17 AM

0 Likes
0
13277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-03-27 02:17 AM

Hi,

If you need urgent support at anytime, I'd recommend you contact your local support office for the quickest response.

Can you let me know what model of UPS this is? I am looking for the model number on the white sticker on the back or bottom. It sounds like a BR or BX something but it may be a region specific model where F04 is triggered by a certain threshold or something that is different from other units.

From the general information I've found, it appears if it continues that the unit may need to be replaced but depending on what is causing it, the root problem may damage any new or replacement UPS too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore