Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84525members
353768posts

Pellet Stove Power Conditioning

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
joebiodiesel_apc
Cadet
0 Likes
2
188

Pellet Stove Power Conditioning

This was originally posted on APC forums on 12/10/2011


I have a Generac 6500W Generator that I use as power backup at home. It easily runs all the loads in my house when the power goes out, and I don't have any problems running my Dell desktop or flat screen TV on it. I asked the manufacturer of my wood pellet stove(Quadrafire) if it was safe to run on my generator, and they advised against it without using some type of power conditioning. They stated they wouldn't warranty any board that was ruined on a generator or inverter. I have been looking at the H15 and J15 power conditioners. I don't need any type of battery backup. Just good, clean power so I don't smoke a $750.00 control board. The stove probably doesn't use more than 8 or 9 amps to get started, and less than that to run, but I'd use it for all my electronic equipment when the generator is running.

Any advice gladly accepted.

Thanks,

Joe


Accepted Solutions
voidstar_apc
Janeway
Janeway
0 Likes
0
188

Re: Pellet Stove Power Conditioning

This was originally posted on APC forums on 12/12/2011


The down side of using a line-interactive UPS for ensuring a clean sine-wave to your equipment is that it will do so by depleting its battery. We have online double-conversion UPS products that regenerate a clean electrical waveform from the generator, but those start at higher power levels and therefore may not be cost effective for this use.

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
188

Re: Pellet Stove Power Conditioning

This reply was originally posted by Angela on APC forums on 12/12/2011


hi joe..i imagine you'd need something like a pure sinewave UPS to avoid ANY damage to the stove. using just a power conditioner might help a little bit but it might not resolve ALL of the potential output issues from a generator. if it were me, i might check out a pure sinewave UPS - something like SMT1500 or SMX1500. You might be ok with an SMT1000 or SMX1000 too depending on that start up amperage you mentioned.

if you really don't want the UPS, the H10 and H15 are audio video type of power conditioners and i don't think that we have anything else really close. this will boost and trim voltage for you depending on if its too high or too low.

voidstar_apc
Janeway
Janeway
0 Likes
0
189

Re: Pellet Stove Power Conditioning

This was originally posted on APC forums on 12/12/2011


The down side of using a line-interactive UPS for ensuring a clean sine-wave to your equipment is that it will do so by depleting its battery. We have online double-conversion UPS products that regenerate a clean electrical waveform from the generator, but those start at higher power levels and therefore may not be cost effective for this use.