New battery pack installed on XS 1000, now gives three beeps when laser printer warms up

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • New battery pack installed on XS 1000, now gives three beeps when laser printer warms up
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:55 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
2
885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:55 AM . Last Modified: ‎2024-03-27 12:39 AM

New battery pack installed on XS 1000, now gives three beeps when laser printer warms up

And the first thing everyone is going to ask, yes, I have the printer on a Surge Only outletsmile

I have the printer, a Brother laser printer, hooked up to one of the surge only ports, just like I had it before. And before the battery replacement, when the printer would go into warm-up, there was nothing. Now when the printer goes into warm-up, I get three beeps and oddly the input voltage shows zero(!) and the battery indicator sometimes goes from five bars to four bars.

Now just to be thorough (retired engineer here) I switched the printer to a battery backup outlet and turned it on. As expected, I got a single continuous beep, which is what I think I would expect as the printer was drawing too much wattage. I placed it back on the Surge Only outlet.

And this is not a consistent behavior. If the printer hasn't been off for too long, when it starts warming up there is no beeping but the input voltage does drop. It seems that the beeping only occurs if the printer has been off for quite a while and therefore has cooled down.

So I'm thinking here that this isn't a big problem, maybe just something that is coincident with the printer pulling so much power that the input voltage to the APC drops to zero which causes the three beeps? The PDF users guide and operating manual don't reference anything that causes three beeps. I'm just wondering if someone else has come across this behavior.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:39 AM

Well, I'm glad I came here and asked! Good to know this, thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:55 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:55 AM . Last Modified: ‎2024-03-27 12:39 AM

Hi James,

This is definitely an issue with the current draw from the Laser Printer. This device should never be connected to the UPS Battery Outlets or Surge Only Outlets.

Please check the following document regarding Laser Printers.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:39 AM

Well, I'm glad I came here and asked! Good to know this, thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore