Overload Protector Button stays outside

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Overload Protector Button stays outside
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

0 Likes
3
3425
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

Overload Protector Button stays outside

Today I was replacing the battery of a 750XL, we use at work, I didn't unplug the power, and just hot swapped the battery, however I removed all the load from the UPS, only the Ac was connected, everything was going ok, I unplugged the old battery and plugged the new one,at this moment the panel was on,  but while I was closing the cover panel, the UPS shutdown. I tried connecting the old battery back, not luck, unplug and plug back the AC, not luck, push all the buttons for over 10 seconds, not luck, however I noticed that the UPS in someway is giving power since the Network card is powered on, when the UPS in unplugged and the battery is connected (new one/ old one). I also noticed that Overload protector button stays all the way out, instead of 1/4'. I tried to push it in, but of course it doesn't stays in. Please let me know what can I do, why my problem happened, and what does it mean?

Regards,

Emmanuel

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • button
  • overload
  • protector
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

0 Likes
0
3416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

Looks like the UPS itself have failed. You might have to consider replacing the UPS itself. Contact Schneider Electric tech support for the options: 800-800-4272

Vinay

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

0 Likes
0
3416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

Hi Emmanuel,

I would suggest a brain dead test on the UPS to reset it. Here is the procedure

1) Turn off and unplug UPS from wall
2) Press and hold the OFF button again
3) You may see a quick flash of the LED's and you should hear an audible ""click"" from the UPS.
4) Plug UPS back into the wall and turn UPS back on

Once you reset the UPS, please try to turn it on again. If the issue still persists, please let me know the reason behind replacing the battery and how long this UPS in operation. If you are monitoring the UPS through the software please provide the event and data logs and also let me know the exact model number of the UPS which is on the white bar code label located on the rear of the UPS.

I would also require the replacement battery model and serial number

Thanks and regards,

Vinay

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

0 Likes
0
3416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

Hello Vinay,

I did the brain test, it didn't do anything, the UPS seems to be "dead" there is no audible sounds or lights at all in the electronic panel. The reason behind replacing the battery was that, it stopped working, well the SNMP message that we got since a while ago said "there is a faulty battery", so that was the reason for replacement. 

The model is SUA750XL

Serial number is : AS0939140394

The replacement battery model and serial number are:

MODEL :RBC7

SERIAL NUMBER is: 7A1634L29638

Regards,

Emmanuel

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

0 Likes
0
3417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

Looks like the UPS itself have failed. You might have to consider replacing the UPS itself. Contact Schneider Electric tech support for the options: 800-800-4272

Vinay

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore