Is my device defective? How does AVR work? When should AVR turn on/off?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is my device defective? How does AVR work? When should AVR turn on/off?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

0 Likes
2
1993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

Is my device defective? How does AVR work? When should AVR turn on/off?

I have a BX1500G.  The power at my outlet is typically at 121volts but does drop regularly down as low as 108 volts.  This usually last about 5 to 10 seconds but sometimes last longer.  I haven't see the AVR light on yet and im beginning to wonder is my device is defective.  The only thing stated the manual is, "Automatic Voltage Regulation +11.5% Boost Only". 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

0 Likes
0
1993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

That was a great explanation.  It would be nice to add this to a documents page on the APC site (not the forum).  I finally got the AVR to switch on.  I switch on my unit ended up occuring around 101v.    Thank you for the help.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

0 Likes
0
1993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

108 volts is low, but it is within tolerance (+/- 10%) for equipment designed for use on a nominally 120 volt system.

The AVR  capability on this model should kick in somewhere around 103 volts AC. I find it interesting that the manual indicates "boost only", as I thought the larger (1300/1500 VA) Back-UPS models had both boost and buck (voltage reduction) capability. Perhaps that has been dropped in newer production?

AVR  works by employing what is known as an autotransformer. An autotransformer  has multiple taps, or voltage outputs, that may be utilized to maintain the output voltage going to a given device at a certain level. The UPS's  microcontroller  would "decide" which tap would be placed into circuit to maintain the line voltage at the desired level. The transformer is rated to perform this operation continuously, so the UPS won't have to switch to battery, and you won't have to worry about shutting your equipment down before the battery would normally run out.

AVR  will turn on automatically when the line voltage drops too low (or in models so equipped, rises too high) and it will turn off automatically when normal line voltage levels are restored.

If AVR  cannot compensate for a low or high voltage condition (it usually only has one or two steps worth of adjustment) the UPS will switch over to battery. At this time the on-battery alarm would sound, indicating that you will eventually have to turn your equipment off.

I'm not sure if APC's   PowerChute  software alerts you when AVR  is being used. Normally, the only sign that AVR  might be operating would come in the form of some relay clicks emitted by the UPS, and the AVR  indicator being illuminated on the unit's status display.

You can adjust the unit's sensitivity from the front panel controls or with PowerChute  software if you are using it. This will also adjust the points where AVR  kicks in.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

0 Likes
0
1994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:56 AM . Last Modified: ‎2024-03-27 12:38 AM

That was a great explanation.  It would be nice to add this to a documents page on the APC site (not the forum).  I finally got the AVR to switch on.  I switch on my unit ended up occuring around 101v.    Thank you for the help.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore