APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:49 AM . Last Modified: 2024-03-27 12:39 AM
I installed a new battery into a BE700G-UK and plugged it in to the mains for a while.
Then I turned on the "Power on". Got 4 short beeps, then some clicking noises, then 2 beeps, then some more clicking, then a single beep, then just various clicking noises, but no more beeping.
Haven't plugged anything into it yet, just in case.
Any idea if this is normal, or if I should be concerned about the clicking?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:49 AM . Last Modified: 2024-03-27 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:49 AM . Last Modified: 2024-03-27 12:39 AM
Hi Simon,
The unit will perform an Online Self test when first powered on. You should hear 4 short beeps as you've indicated along with some clicking. The clicking and beeps following that initial self test sound as if the unit may be transferring to battery for environmental causes. You should be able to adjust the the transfer thresholds in the PowerChute Personal Edition software. These thresholds will widen the range of operation for the UPS and hopefully stop it from trying to transfer all the time.
Secret Squirrel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:49 AM . Last Modified: 2024-03-27 12:39 AM
Thanks Secret Squirrel
I'll give that a try.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.