APC UPS 750 ES

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC UPS 750 ES
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
6
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

APC UPS 750 ES

I bought a new APC brand battery for my 750 ES that I have been having issues with a and it looks like it maybe working better now.

I am still in the testing phase and I connected a lamp with a 60W incandescent bulb to it.  When I turn it on it says it only has a 22 watt load.

Is there a way to fix this to re-calibrate the load on the UPS because it is obviously wrong.

I plugged in other items that I know the load of and it is always way under on the true load.

Joe

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

I am getting the 85 v on plug. When on battery. Plus lights are dim when on battery. Lights go bright and I get 115v when I go back and plug in ups.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

Hi Joe,

The Back-UPS ES 750G / BE750G is a Stand-By UPS. Being that it's Stand-by it can not truly provide accurate load capacity, unless it is operating off the inverter. The load provided while online is only approximate. To see the true load, the UPS should be forced to battery.

Now that being said, depending upon the age of the incandescent light bulb your using you may discover it's not drawing the full specified watt rating. As these bulbs age, the filament is depleted through continuous use resulting in diminished current draw and overall luminance.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

Thanks.

Looks like the investor had failed. On battery I am only getting 85v. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

That may be due to the type of voltmeter you are using.

The UPS produces a step approximated sine wave which can not be accurately measured by a standard voltmeter. These inexpensive meters are often refereed to as Non-True RMS voltmeters which are widely available at any local hardware / automotive store. These meters are only capable of averaging their reading.

When measuring a Pure Sine wave, the True RMS and Non-True RMS meters will give the correct AC reading, however when measuring any waveform other than the Pure Sine wave, the Non-True RMA meter provide a voltage reading much lower than what is present. In some cases it could be as low as 40%.

A True RMS meter will actually have this printed somewhere on the enclosure, unlike a Non-True RMS.

True RMS Volt MeterNon-True RMS

Secret Squirrel

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

I used a fluke true one. 

I also thought it was wrong when the 60w bulb from an incandescent light I had plugged in for a test load was dim when running off battery but bright when I plugged the ups back in. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

Are you measuring between Neutral and Hot while on battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

0 Likes
0
1948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:49 AM . Last Modified: ‎2024-03-27 12:39 AM

I am getting the 85 v on plug. When on battery. Plus lights are dim when on battery. Lights go bright and I get 115v when I go back and plug in ups.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore