Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Is Powerchute required?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Is Powerchute required?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

0 Likes
6
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

Is Powerchute required?

I'm about to purchase a RS1300LCD or RS1500LCD. I prefer minimum software running while I record audio. I'm on XP and I generally disable 3/4th of the standard windows applications that run in the background including the clock, antivirus, etc, etc, etc because each of these apps typically ping the system and can leave tiny ticks/glitches on otherwise pristine audio. So my question is, will I have fully functionality of the UPS if I don't install the Powerchute software? It seems as a minimum there will be USB port in use.

Thanks in advance for your reply.

Wayne

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

I did a little more testing . . . if I set the critical battery alarm action to standby the PC goes to standby as expected. I then tried using the shutdown -s -c "test shutdown" -t 30 command in a cmd window; if you just type shutdown in a cmd window it will show you all of the command line options. That worked fine as well. If I can't get the shutdown alarm action to work properly then I will make the alarm action "no action" and then use the "run a program" setting to run the shutdown command listed above (with different settings). I'll try the shutdown alarm action shortly . . .

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

Hello,

The nice part about the LCD models is that you can make configuration changes with help from the screen and the buttons, where normally PowerChute would be required.

However, if you are looking for graceful shutdown of your computer when the UPS hits a low battery state, you would either need PowerChute or setup the native XP UPS support.

Because it sounds like you would rather go the path of not using PowerChute please see our Kbase on how to setup native:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2497

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

so adding on to what Cap1 said, powerchute is NOT required for the essential function of the UPS. It would provide graceful shutdown which is also available via the native support on XP as Cap1 mentioned previously. the LCD models have a lot of the functionality of powerchute already so they really are nice for your particular situation and not wanting to install the software.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

Thanks for the response. My computer is on only when attended, so I should have up to 3-4 minutes to shutdown my apps and computer when the UPS goes on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:35 PM . Last Modified: ‎2024-03-26 12:16 AM

I'd like to ask a related question - I just installed a BE550R and set it up with native XP (SP3) support. I checked the KB article listed above and everything mentioned there is fine regarding device manager and what I see in control panel. The default setting was "No Action" for Low Battery Alarm and "Standby" for Critical Battery Alarm.

I did not want to leave the Critical Battery Alarm setting at Standby in case of a prolonged power outage so I set it to shutdown, thinking I would get a graceful shutdown of Windows. I'd prefer to not use hiberation (another 2GB of my hard drive gone.) I adjusted the percentages to 85% and 65%, respectively, and did a test. At 85% I got the low battery alarm. At 65% the screen went blank, it looked like a shutdown you get when you just switch off your power supply. When I restarted the PC, Windows Live mail and Folding@home both complained of improper shutdown.

Shouldn't you get a shutdown of Windows with this setting? If so, what should I set differently? I didn't really see any other places to make settings changes . . .

Or is installing Powerchute the only way to get Windows to shutdown properly?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

Hello,

I would test it with PCPE and see where you get. When controlling via Native, Windows is doing whatever it wants to execute a shutdown. I find it difficult to believe though that you'll get a different reaction from installing PCPE which just executes a shutdown - essentially doing the same thing as Native's setup, with bells and whistles.

If you're willing to test that, please let us know the results.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

I did a little more testing . . . if I set the critical battery alarm action to standby the PC goes to standby as expected. I then tried using the shutdown -s -c "test shutdown" -t 30 command in a cmd window; if you just type shutdown in a cmd window it will show you all of the command line options. That worked fine as well. If I can't get the shutdown alarm action to work properly then I will make the alarm action "no action" and then use the "run a program" setting to run the shutdown command listed above (with different settings). I'll try the shutdown alarm action shortly . . .

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore