Is this normal?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is this normal?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

0 Likes
6
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

Is this normal?

I haven't had my unit long, about a week. Yesterday, the power went off for about an hour. When the power went off, my PC was completely shut down. Everything was off. When the power came back on, I checked the status of my unit, and it said that there were 13 minutes remaining and that the unit was charging. I can't figure this out. As far as I can tell, there was no drain on the battery. Where was the power going? Can the unit lose power just because the external power has been lost?

Bill

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:04 AM

0 Likes
0
1265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:04 AM

Bill,

Other than physically powering the UPS off, or it shutting down after battery power is exhausted, the Back-UPS line of products cannot be commanded to power off after completing a shutdown. Normally it will just go to Low Voltage Sleep Mode after completing the hibernation of the PC, and sit there until either power returns, or the battery becomes exhausted. I believe it is that "stuff" to which you refer which is powering the UPS during Low Voltage Sleep Mode.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

Bill,

I guess the next question to clear things up would be, now that I understand that your PC was off, is whether or not the UPS was on at the time?

Do you power it off if the PC is not on? Ideally, when the UPS is used in that manner, the battery may start to discharge slightly because there is no consistent power being provided to it.

However, if the UPS was on powering nothing, it will transfer to battery regardless of a load attached, and will operate on battery for up to 3 minutes with no load or less than 50W attached, before powering itself off.

Obviously that will create a state of "charging" upon power restoration to the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

0 Likes
0
1265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

Bill,

I hope I am correct in assuming when you say that you checked the status of your unit for runtime, you checked through PowerChute. Is Hibernation enabled on your system? Is the UPS data cable running through an externally powered USB hub? Within PowerChute, do you have it set to shutdown after X minutes on battery, or once there are X minutes remaining (basically, one is power saving, the other is max runtime)?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

K.M.P.,

I wan't really sure how to configure it. Yes, it was Power Chute that told me I had 13 minutes remaining. When I look at the Runtime screen, I have "Keep my computer running as long as possible" selected, and Shut down when backup power is 5 minutes. But my computer wasn't running when the powere went off, it was shut down and turned off.

Bill

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

0 Likes
0
1265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:15 AM

KMP,

Yes, the unit itself was on. I normally leave it on all of the time, not just when I am using the PC.

Bill

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:04 AM

0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:04 AM

KMP,

Gradually, I think I am beginning to understand the situation and what is happening. Inside the unit, in addition to the battery, there is "stuff." This "stuff" draws power (when the unit is on) and if there is no power coming in, the "stuff" will draw power from the battery. So my next question is, can the unit turn itself off, and if so, how do I set it up to turn itself off?

Bill

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:04 AM

0 Likes
0
1266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:36 PM . Last Modified: ‎2024-03-26 12:04 AM

Bill,

Other than physically powering the UPS off, or it shutting down after battery power is exhausted, the Back-UPS line of products cannot be commanded to power off after completing a shutdown. Normally it will just go to Low Voltage Sleep Mode after completing the hibernation of the PC, and sit there until either power returns, or the battery becomes exhausted. I believe it is that "stuff" to which you refer which is powering the UPS during Low Voltage Sleep Mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore