So the utility voltage in my country is 230-240V at nominal, but in my area it goes quite high (around 265V) at night in the colder months as not many people switch on their Aircon at that time.
The PSU in my PC is rated for 100-240V input and it's said that +10% margin for input VAC is usually built in for most PSUs, meaning up to 264V.
So I've set the high transfer point of my Smart-UPS SUA1500I-IND to kick in at 263 VAC.
My utility voltage may remain at those elevated levels for several hours every night & into the early morning hours. So I'm wondering if AVR Trim being active for that long every day is going to result in any problem for my UPS?
If it helps, it's going to be pretty rare for the equipment connected to the UPS to be under any heavy load during those hours.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-23 09:28 AM
Your asking the wrong question. The system can run forever in the AVR Trim / Boost mode.
What you’ll eventually see is a (Relay Weld) fault code / error! ☝️
As every time the system transfers over to Trim / Boost. This action wears down the relays and ultimately causes relay contact arcing.
This is why all APC UPS have a dedicated error / fault code for this specific problem. ☹️
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-23 09:28 AM
Your asking the wrong question. The system can run forever in the AVR Trim / Boost mode.
What you’ll eventually see is a (Relay Weld) fault code / error! ☝️
As every time the system transfers over to Trim / Boost. This action wears down the relays and ultimately causes relay contact arcing.
This is why all APC UPS have a dedicated error / fault code for this specific problem. ☹️