Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How do you test these batteries?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: How do you test these batteries?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

0 Likes
2
2598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

How do you test these batteries?


My UPS's all seem to use the standard 12 volt size that are two batteries in series.  I recently tested my XS 1500 with a MacPro on it. The second I unplugged the UPS the computer went down/off.  So I go to replace the batteries.

The pair of new batteries tested at 12.6 volts each, but the old batteries that wouldn't power up even a second with a disconnect, both measured 13.5 volts.  This is crazy to my way of thinking. How can they have more voltage than the new ones and still not work?  If it's the current we're concerned about and not voltage, how do you measure that? It would have to be under a load wouldn't it?  How do you test to make sure it's the battery and not just a UPS gone bad?  This has always eluded my logic between the batteries  being good or bad and the UPS being good or bad.  There must be some easy way to test them. Can you suggest a good method?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

0 Likes
0
2598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

Yes it does seem counter intuitive.  It has to do with the internal resistance of the cells and connections within the battery.  An old and worn out battery will have high internal resistance so that even a relatively low external load will cause a considerable amount of voltage to be dropped across the battery itself and the load will get little to no current.  With a load connected, the bad battery's voltage will drop from the 13.5 you measured.  The good battery, the one measuring 12.5 volts but with low internal resistance, will allow much more voltage to be provided to the load and, therefore, higher current to flow.  The new battery, when charged properly to float level, will eventually reach the 13.5 or 13.6 you measured across the bad battery.  Hope this helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

0 Likes
0
2598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

connect bulb 60w or 120w in parallel with battery and test, if voltage low quickly , the battery is bad

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

0 Likes
0
2598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

Yes it does seem counter intuitive.  It has to do with the internal resistance of the cells and connections within the battery.  An old and worn out battery will have high internal resistance so that even a relatively low external load will cause a considerable amount of voltage to be dropped across the battery itself and the load will get little to no current.  With a load connected, the bad battery's voltage will drop from the 13.5 you measured.  The good battery, the one measuring 12.5 volts but with low internal resistance, will allow much more voltage to be provided to the load and, therefore, higher current to flow.  The new battery, when charged properly to float level, will eventually reach the 13.5 or 13.6 you measured across the bad battery.  Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore