False overload alarm or defective unit ? (Back-UPS ES 700)

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • False overload alarm or defective unit ? (Back-UPS ES 700)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

0 Likes
4
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

False overload alarm or defective unit ? (Back-UPS ES 700)

Hi,

I have two identical Back-UPS ES 700 that manifest the same problem (mention: I changed the batteries thinking they were the problem):

I plug in the ups

I start the ups (with no load)

I let the battery charge 24h with no load

powerchute tells me the battery is full and approximates it to 42 minutes of availability in case of power failure

I plug in any low power device in the ups' battery backup (ex. any one of the following: cell phone charger, external 3.5"HDD, led monitor)

I unplug the ups from mains

the ups starts making a continuous sound as if it were overloading, the device powered by the ups loses power, the status led loses its intensity as if it were barely lit, powerchute loses conectivity with the ups and after a shot time (maybe 30 seconds) the ups turns off.

I unplug the consumer from the ups

I plug the ups back into the mains

all comes back to normal

powerchute tells me the battery is at 96%

.....

I tried changing the sensitivity and voltage settings to low and 167-278 volts and disabled the battery backup alarms at all times but it didn't help

Not to be misunderstood, I tried to power my workstation too (350W) with the same results.

now i'm asking: false overload alarm or defective ups ?

PS: suggestions anyone?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

0 Likes
0
1836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

Do you see anything on the PowerChute status section in the brief 30 seconds or does the computer start to shutdown?

Definitely does not sound normal and then even worse, there are two units doing this.

What happens if you do this with no load and unplug the UPS from mains, same behavior?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

0 Likes
0
1836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

Have you tried this test without the USB cable for PowerChute connected?

Also, can you turn it off and then "cold start" it? Meaning start it off of its own battery power? To do this, turn it off, unplug it from the wall, then hold down the power button to start the unit off of battery. Then try plugging something to see what it does.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

0 Likes
1
1835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

Hi,

I have two identical Back-UPS ES 700 that manifest the same problem (mention: I changed the batteries thinking they were the problem):

I plug in the ups

I start the ups (with no load)

I let the battery charge 24h with no load

powerchute tells me the battery is full and approximates it to 42 minutes of availability in case of power failure

I plug in any low power device in the ups' battery backup (ex. any one of the following: cell phone charger, external 3.5"HDD, led monitor)

I unplug the ups from mains

the ups starts making a continuous sound as if it were overloading, the device powered by the ups loses power, the status led loses its intensity as if it were barely lit, powerchute loses conectivity with the ups and after a shot time (maybe 30 seconds) the ups turns off.

I unplug the consumer from the ups

I plug the ups back into the mains

all comes back to normal

powerchute tells me the battery is at 96%

.....

I tried changing the sensitivity and voltage settings to low and 167-278 volts and disabled the battery backup alarms at all times but it didn't help

Not to be misunderstood, I tried to power my workstation too (350W) with the same results.

now i'm asking: false overload alarm or defective ups ?

PS: suggestions anyone?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

0 Likes
0
1837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 PM . Last Modified: ‎2024-03-20 05:58 AM

Do you see anything on the PowerChute status section in the brief 30 seconds or does the computer start to shutdown?

Definitely does not sound normal and then even worse, there are two units doing this.

What happens if you do this with no load and unplug the UPS from mains, same behavior?

Reply

Link copied. Please paste this link to share this article on your social media post.

maxpower
Crewman maxpower
Crewman

Posted: ‎2022-07-05 01:09 PM

In response to Anonymous user
0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-05 01:09 PM

I currently (Jul-2022) face the exact same issue.

 

A Back-UPS ES 700 makes an anoying loud continous sound when pulling the mains plug with a testing device (e.g. lamp) connected to the UPS. When unplugging the lamp, the sound stops.

 

The ES 700 does not tell to replace the battery, though I think I should, it already 6 years old...

 

Why was your question marked "solved"? I see no solution there.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of