Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

APC SMX750i Failing Firmware Upgrade

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC SMX750i Failing Firmware Upgrade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2022-05-14 05:10 AM

0 Likes
3
3222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-14 05:10 AM

APC SMX750i Failing Firmware Upgrade

Hello,

          I have an issue where a SMX750i is failing upgrade at 7%, obviously it starts the process and switches the UPS off, then that's where it stays.

I have installed a new battery pack - still fails the same

I have tried with UPS switched off - still fails the same

 

I would like to think I am doing everything right as I have no problem with other APC UPS's when using the same FirmwareUpgradeWizard_v4.2.1

UPS Firmware details:

UPS 09.1

MCU 09.1

UBL50E.7

MBL 06.0

 

The tool automatically selects SMT20UPS_10-2.enc

 

Any assistance would be great as I would really like to be able to enable the Modbus communications that the later firmware supports.

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2022-05-18 11:00 AM

In response to APC_Matt
0 Likes
1
3104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-18 11:00 AM

Hi Matt,

             Thanks for the advice, I must admit I did try and download v4.3 but that was only available outside of UK, seems like they have released it here now, the firmware file is the same.

 

What I did read on here is that someone had issue and were advised to do a factory reset if they had the 5 button version, I done that and found that upgrade via USB still failed but via serial then worked, so yesterday I was successful lifting it to v10.2 and giving me the Modbus communication.

 

Thanks again, and hopefully this will help anyone else with similar issues.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
APC_Matt
APC_Matt Contributor
Contributor

Posted: ‎2022-05-18 01:55 AM

0 Likes
2
3119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-18 01:55 AM

Hi Ghoster

Could you try the latest firmware upgrade wizard 4.3.0 and see if that helps.

https://www.apc.com/uk/en/faqs/FA279197/ 

If it doesn't I can decode the FUW.log file it produces and see if that highlights the issue.

 

Thanks

 

Matt

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-05-18 11:00 AM

In response to APC_Matt
0 Likes
1
3105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-18 11:00 AM

Hi Matt,

             Thanks for the advice, I must admit I did try and download v4.3 but that was only available outside of UK, seems like they have released it here now, the firmware file is the same.

 

What I did read on here is that someone had issue and were advised to do a factory reset if they had the 5 button version, I done that and found that upgrade via USB still failed but via serial then worked, so yesterday I was successful lifting it to v10.2 and giving me the Modbus communication.

 

Thanks again, and hopefully this will help anyone else with similar issues.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

robmir_apc
robmir_apc
Contributor

Posted: ‎2022-07-11 07:52 AM

In response to Anonymous user
0 Likes
0
2879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-11 07:52 AM

I service several smart APC UPS and when updating their software I use their serial port and a computer with a direct to the motherboard serial  port and never a USB to Serial adapter.  Since the motherboard has a com1 socket I sourced a  rear backplate with the 9 pin male connector fixed to it, it's ribbon cable and it's matching  plug to the motherboard socket and installed the plate on my computer case. Unfortunately most of the  newer motherboards lack a rear serial port. 

 

So far it rarely give me a failed update and I highly recommend this way. I know it's old school but it works !!!!!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore