Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Dual Power Supply Server with one on a UPS one not

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Dual Power Supply Server with one on a UPS one not
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:19 AM . Last Modified: ‎2024-03-27 01:50 AM

0 Likes
7
2916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:19 AM . Last Modified: ‎2024-03-27 01:50 AM

Dual Power Supply Server with one on a UPS one not

I recently had a conversation with a colleague on the issues of providing power to a server with dual power supplies. He argued that providing power to a server by plugging one of its power supplies directly into a plug strip and plugging the other power supply into a UPS that was then plugged into that same power strip would cause a shift in phase of the power being provided to the server which would in turn cause a decrease in the life expectancy of those server power supplies. I don't doubt that the UPS could change the phase of the power being sent to the server. However, I believe that modern power supplies convert the incoming AC signal to a DC voltage which they then use to construct new pulsed AC waveforms to generate the multiple internal voltages needed which are then heavily filtered before being sent on to the server circuitry. If this is true, then the original incoming waveform phase shift between sources is not an issue and would not be detrimental to the longevity of the power supplies. Can anyone give us a definitive authoritative answer?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • expectancy
  • life
  • longevity
  • phase
  • power
  • shift
  • supply
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

0 Likes
0
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

HI,

I asked one of our engineers that work on the Smart-UPS product line. He said it would not make any difference because the power supplies work independently of one another. There should be no increase of mean time between failures by plugging one supply into a PDU and the other into a UPS. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:19 AM . Last Modified: ‎2024-03-27 01:50 AM

0 Likes
0
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:19 AM . Last Modified: ‎2024-03-27 01:50 AM

"Definitive and authoritative" probably don't apply to an answer to this question.  Depending on the type of UPS you have, the UPS may "reconstruct" the incoming waveform when on commercial power or simply pass the input to the output through an internal switching (relay) arrangement.  In the case of passing the input through to the output there wouldn't be any appreciable phase shift at all unless you are concerned about the additional length of the wiring inside the UPS itself.

In any event and although I could be wrong, I don't think today's modern power supplies configured redundantly within a server "care" one bit about the phase of the incoming AC waveform.

This could end up in a discussion much like happens when the advocates of single rail vs. multiple rail power supplies get together over a brewski.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:19 AM . Last Modified: ‎2024-03-27 01:50 AM

0 Likes
0
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:19 AM . Last Modified: ‎2024-03-27 01:50 AM

Hi,

We have Kbase FA158852 "Using surge strips with APC's Back-UPS and Smart-UPS products". 

There would not be a phase shift however there could be a short, disruption of ground. If you are going to use a plug strip you should plug 1 power supply into it, the other into the UPS, and the UPS directly into the wall outlet. It would be even better if the wall outlets the plug strip and UPS are connected to are on different circuit breakers to mitigate a single point of failure. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

0 Likes
0
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

Thanks Joe: I agree that it is most likely that the system doesn't care but I was hoping to get some kind of documented opinion.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

0 Likes
0
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

Thanks Bill, good information but not quite what I'm after. Our situation is we are building a new server room. It will have three racks with three independent hard wired power connections. These power multiple outlet power strips inside each rack. My plan is to plug a UPS into this power strip and plug one of the server redundant power supplies into the UPS and the other directly into the power strip. No surge suppression at this point. While trying to determine the size and number of UPS devices we got into the discussion mentioned above. We didn't want to create a single point of failure by connecting both power supplies to the same UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

0 Likes
0
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

It is quite likely that the power coming into your building is either 3-phase or two phase legs of the three. Normal circuit breaker panels alternate between supply feeders in either an ABCABCABC OR ABABABAB sequence, so if the two power supplies in your device are fed from different circuits, it is quite likely they're on different phases already.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

0 Likes
0
2918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

HI,

I asked one of our engineers that work on the Smart-UPS product line. He said it would not make any difference because the power supplies work independently of one another. There should be no increase of mean time between failures by plugging one supply into a PDU and the other into a UPS. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

0 Likes
0
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:50 AM

Thanks Bill. I appreciate your taking the time and trouble to find an answer for us.

Ron

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of