BE550 no power on battery backup outlet

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE550 no power on battery backup outlet
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

0 Likes
7
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

BE550 no power on battery backup outlet

The BE550 just passed the 3 year warranty period, and suddenly, no power on the outlet of battery backup + surge protection.

LED is green and no other alarm sound, all behave normal.

During the power on, there was a period of having power on the outlet, but just for a few seconds.

The strange thing is, at this condition, if the AC input is disconnected, there is power on these outlets and connected device works fine, with periodic alarm to indicate the AC line is off.

I tried only putting a switcher, a few watts load, on the outlet and the symptom is the same.

The surge protection only outlets are working fine.

Any idea on this problem?

Thanks!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • be555
  • no
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

0 Likes
0
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

Hi William,

thanks for your advice. I'll keep an eye on the solder joints.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

0 Likes
0
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

Hi Congshi,

I would try what we call a brain dead. Turn off the unit, unplug it from the wall, and disconnect the battery. Wait about 30 seconds. Re-connect the battery. At this point I would turn the unit on via battery power by holding the power button. If it turns on (which it sounds like it should based on your description) verify there is power from the outlets and then connect it to the wall plug. At this point it should transfer off battery power. If it stays on battery power that tells me that it does not see good input power. If it transfers off battery power (the beeps stop) and the power from the battery outlets goes out I would think that there is some sort of short internal of the unit. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

0 Likes
0
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

Hi Michael,

Thanks for the advice.

Following your steps, the unit turns on by battery normally, the outlets have power. Once the AC cord plugged in, with one click sound, the power is disconnected from the outlets. So it must be what you said “there is some sort of short internal of the unit”.

Would you elaborate a little for “there is some sort of short internal of the unit”? Some parts dead?

Thanks again for the help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

0 Likes
0
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

Before you give up on the unit, check its built in circuit breaker to see if it might have tripped. (Of course, if it did, it's also possible that the circuit breaker did not survive the experience. Sometimes they don't.)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

0 Likes
0
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

Hi Michael,

The problem has been fixed, thanks for the advice.

I opened the box. Since I just saw one relay, I measured the relay working voltage, which was just above 10 volt when AC in. Then I saw some brownish stuff on the PCB board along the relay driver. I wiped them off with swab and rubbing alcohol. When turning it back on, the relay working voltage is about 13 volt and the outlets have the power!

So the problem is the leakage in the relay driver, which makes the drive has no enough power to drive the relay properly. Although the click sound is heard, it just turns off the battery power but not contact well to the AC line.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

0 Likes
0
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

Hi William,

Thanks for the reply.

Since the surge protection only outlets are working fine, it shouldn’t be the circuit breaker. The circuit breaker control all AC input.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

0 Likes
0
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

Sorry about that, I misread what you wrote. My next thought was that of a relay or relay driver fault. It might not be a bad idea to touch up the solder joints on that, if you're equipped to do so. My guess is that while cleaning the pins couldn't have hurt, the solder joints could probably stand to be reflowed as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

0 Likes
0
2235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:20 AM . Last Modified: ‎2024-03-27 01:49 AM

Hi William,

thanks for your advice. I'll keep an eye on the solder joints.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore