Desktop UPS with controllable outlets?
Hi,
Which models of UPS have the ability to control the outlets. I want the ability to cut the power to certain outlets via the web interface. These UPS units are remote and space is limited so dont want to use a smart PDU.
If i have a crashed device, i need the ability to cut the power\enable the power again.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2808:28 AM. Last Modified: 2024-03-2603:24 AM
Hi,
Smart-UPS SMT and SMX models have switchable outlet groups. Example SMT1500 has 2 groups. A main that controls all outlets and a switched. The switched can be power off and on individually. When the main is switched off and on the switched also is powered off and on.
A SMX1500 has 3 switched outlet groups. They all work independently of each other as there is no main.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2808:28 AM. Last Modified: 2024-03-2603:24 AM
Hi,
Smart-UPS SMT and SMX models have switchable outlet groups. Example SMT1500 has 2 groups. A main that controls all outlets and a switched. The switched can be power off and on individually. When the main is switched off and on the switched also is powered off and on.
A SMX1500 has 3 switched outlet groups. They all work independently of each other as there is no main.