Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Considering UPS/power condition for my whole house

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Considering UPS/power condition for my whole house
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
8
4696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

Considering UPS/power condition for my whole house

Hey all,

I live in an area that seems to blow lightblubs like bubbles popping in the bathtup, and those little halogens start to get expensive rather quickly!

So, in the spirit of longevity for both my bulbs, electronics, and everything else I'm considering a UPS/power conditioning system for my house.

I currently have 100 AMP service and use as much as 80 kWh/day, as low as 40 and seems to average about 55. If I went with the UPS option, I'd want to base it on 55 kWh/day - and require no more than 10 minutes backup time.

Form this information I have NO idea how to "size" the appropriate equipment and what the relative cost for such a system would be. This is a dip into the unknown... as is my next comment.

I'm also considering adding some alternative power to my residence, either with a Windmill or Solar panel(s) - possibly both over time. I'd like the system installed to allow for the expandability of such power sources without having to reinvent the wheel when it happens. I'm also not opposed to this being a 'homegrown' solution if my plans don't fall within any pre-packaged option available.

Thanks for your attnetion, thoughts and any assistance you can provide 🙂

[aidanenos@rogers.com]

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • building
  • conditioning
  • green_grid
  • residential
  • surge
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

I have been considering a similar option using a mix of grid pwr
and solar. I need to figure how to install a UPS unit along with
grid and solar mix. I'd need 30kwh average/day at max - less than
20kwh/day normal ops. I'm in talks with a rep from SPP and
a private contractor @TT. I'll post updated info and their suggestions
when I get a better understanding of the project. APC Back UPS
would be an integral part of overall system. Best of luck.
slowpoke7@gmail.com

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

Hi Slowpoke,
You posted to this APC discussion forum a request for info on whole house
battery backup. ??? Do you really want to try to power up your home using
a battery backup system? It is my understanding that most small to medium
ups's are square wave output, not a true sinewave as is supplied by your
local power company. Your PC, Printer, Monitor, TV, don't care if their power
is square or sine. But your furnace,refridgerator, sump pump, washing machine
dryer do care!!! They require voltage in the form of a SINEWAVE. So if your
considering using batteries to backup your whole house in the event of a
power outage of long duration, then you should make sure it has a TRUE
SINEWAVE output of the correct frequency for your area. There are two basic
types of battery backup systems. The first is called "OFFLINE" backup UPS.
The keyword here is "offline". It means the batteries are never ever used for
99% of the life of the backup system. That is if you have a reliable power
company. If not, then that 99% becomes 98, 97, 96% because when the
lights go out the electronics inside the backup switches over to battery mode
and starts up the inverter to provide a cheap squarewave to your PC, ETC.
The second type of backup is what I like to call a true "UNINTERRUPTABLE
POWER SUPPLY" !!! The backup UPS is ALWAYS RUNNING ON THE
BATTERIES!!! The only thing the power company needs to do is provide
the voltage and current to keep the batteries charged no matter what the
load may be. The Key here is this. It is completely transparent to the user!!
This type of AC Sinewave power backup is expensive. Most commonly used
by hospitals and big corporations and other emergency services organizations
worldwide. The cost of these systems could be (only a guess) $900/kw on up
to $2000/kw of power. There are companies that specialize in these types
of battery backup. You may want to see what Chloride Systems has to offer
just for laughs and giggles. I don't know if they would even consider doing
anything residential. I know they bought up and now occupy the building
that ONEAC corp was in. They too were in the battery backup business.
Well, I hope that I have supplied some information that will be of use to
you.

lmistyrel@aol.com

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

Have you complained to the power company? Try not to spend your own money to correct something utility might correct given enough persistence. That would be a good start. A large double conversion UPS is going to be too costly to run/maintain for a home user.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

Welcome to the community!

When we size a UPS we would want to know the total power draw at any one time in watts. You would want to take the highest possible load at any one time for UPS sizing, then add 20-40% capacity to give you some room to expand and also to be safe against inrush current. Also, I'm assuming this is a single phase 100amp service?

UPS's of this size are doable, but costly for home implementation. After you confirm the above questions I can give you some ideas, but to give you a ballpark, something this size will likely be close to $10k

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

I have been considering a similar option using a mix of grid pwr
and solar. I need to figure how to install a UPS unit along with
grid and solar mix. I'd need 30kwh average/day at max - less than
20kwh/day normal ops. I'm in talks with a rep from SPP and
a private contractor @TT. I'll post updated info and their suggestions
when I get a better understanding of the project. APC Back UPS
would be an integral part of overall system. Best of luck.
slowpoke7@gmail.com

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

Hi Slowpoke,
You posted to this APC discussion forum a request for info on whole house
battery backup. ??? Do you really want to try to power up your home using
a battery backup system? It is my understanding that most small to medium
ups's are square wave output, not a true sinewave as is supplied by your
local power company. Your PC, Printer, Monitor, TV, don't care if their power
is square or sine. But your furnace,refridgerator, sump pump, washing machine
dryer do care!!! They require voltage in the form of a SINEWAVE. So if your
considering using batteries to backup your whole house in the event of a
power outage of long duration, then you should make sure it has a TRUE
SINEWAVE output of the correct frequency for your area. There are two basic
types of battery backup systems. The first is called "OFFLINE" backup UPS.
The keyword here is "offline". It means the batteries are never ever used for
99% of the life of the backup system. That is if you have a reliable power
company. If not, then that 99% becomes 98, 97, 96% because when the
lights go out the electronics inside the backup switches over to battery mode
and starts up the inverter to provide a cheap squarewave to your PC, ETC.
The second type of backup is what I like to call a true "UNINTERRUPTABLE
POWER SUPPLY" !!! The backup UPS is ALWAYS RUNNING ON THE
BATTERIES!!! The only thing the power company needs to do is provide
the voltage and current to keep the batteries charged no matter what the
load may be. The Key here is this. It is completely transparent to the user!!
This type of AC Sinewave power backup is expensive. Most commonly used
by hospitals and big corporations and other emergency services organizations
worldwide. The cost of these systems could be (only a guess) $900/kw on up
to $2000/kw of power. There are companies that specialize in these types
of battery backup. You may want to see what Chloride Systems has to offer
just for laughs and giggles. I don't know if they would even consider doing
anything residential. I know they bought up and now occupy the building
that ONEAC corp was in. They too were in the battery backup business.
Well, I hope that I have supplied some information that will be of use to
you.

lmistyrel@aol.com

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

Just a note here on the above response. Anything besides APC's "Back UPS" and "Smart UPS SC" lines have a pure sine wave output. Anything large that would be for a house does not have a "step approximated sine wave. (or modified square wave)."

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

I think in this instance, to power something as an entire residence and to provide overhead for inrush currents on a freezer, fridge, washer, dryer, etc., we'd be looking ad spec'ing out something like a Symmetra LX. The problem therein lies that if you put it near the service panel to hardwire in/out, what're you going to do about cooling as well? This is why APC probably doesn't manufacture an entire residential UPS system. However, Smart-UPS deployed with something like a Honda generator may actually get the job done for a lot cheaper.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

Have you complained to the power company? Try not to spend your own money to correct something utility might correct given enough persistence. That would be a good start. A large double conversion UPS is going to be too costly to run/maintain for a home user.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

0 Likes
0
4696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:38 PM . Last Modified: ‎2024-03-21 03:34 AM

That does seem a bit costly to provide battery backup to the whole house. However, what about line conditioning only? I know APC has the whole house surge protectors that install at the service panel but they don't appear to have line conditioning. I have also seen out on the web several people pushing power conditioning and power saving devices that will connect to the service panel. Many of these tout energy savings of 10-25% while providing surge suppression, line conditioning, EMI/RFI noise reduction etc. I am curious if anyone has any feedback on these devices or if APC does offer a similar product for the whole house.

I run a computer business out of my home and my end goal is to save money while providing consistent power to all the equipment I have in my home from computers to appliances.

Any feedback or recommendations is appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

davidkayle
davidkayle
Cadet

Posted: ‎2025-10-27 02:22 PM

0 Likes
0
201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-27 02:22 PM

Hey there,

You’re definitely thinking along the right lines by addressing power quality before adding renewables. Frequent bulb failures usually point to voltage fluctuations or poor power factor, which a good power conditioning setup can smooth out nicely.

Given your 100A service and average daily use of around 55 kWh, you’re dealing with a decent-sized load. To size a UPS/power conditioner for the whole house, you’ll want to start by looking at your peak demand (usually around 10–12 kW for most homes of that usage) rather than daily energy use. Since you only need about 10 minutes of backup, you’re not looking at massive battery capacity—just enough to bridge outages or voltage dips.

A practical approach might be a hybrid inverter system that combines UPS functionality with the ability to integrate solar or wind later. This lets you add battery storage or renewables without replacing the main hardware.

If you’re not sure where to start, I’d suggest reaching out to Energy Control System—they specialize in power conditioning, surge protection, and renewable integration. They can assess your service panel, look at your load profile, and help design something expandable and cost-effective.

Good luck with the setup! Once you stabilize your incoming power, you’ll likely notice a big improvement in both lighting and the lifespan of your electronics.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore