Computer freezes since installing UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Computer freezes since installing UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:23 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
16
3918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:23 PM . Last Modified: ‎2024-03-26 01:19 AM

Computer freezes since installing UPS

I bought the Back-UPS BX1300 and I have been having Problems with the Computer freezing since. I have been in touch with the Support team and have uninstalled the Program that comes with it and downloaded the new version. Un installed that and I am still having the same Problem. My Computer freezes every so often It could be 2 Days or 2 Weeks in between. This has been going on now for two months. I don't know what to do or how to find out what is causing it. I would be so happy if someone could help.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:18 AM

0 Likes
0
3917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:18 AM

I bought the Back-UPS BX1300 and I have been having Problems with the Computer freezing since. I have been in touch with the Support team and have uninstalled the Program that comes with it and downloaded the new version. Un installed that and I am still having the same Problem. My Computer freezes every so often It could be 2 Days or 2 Weeks in between. This has been going on now for two months. I don't know what to do or how to find out what is causing it. I would be so happy if someone could help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 16
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

Hello,

It definitely looks like a problem with the PC having the wrong software. Uninstall that, and use the following link:

ftp://ftp.apc.com/apc/public/software/windows/xp/pcpe/200/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

Sorry for the Mistake. It is PowerChute Personal Edition 2.0 that I downloaded and installed. It is American Power Conversion Corporation File version 2.11.15.0. That is were I made the Mistake. I have un-installed the Software and still have the problem with freezing.. Thank You for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

What OS and what version PowerChute Personal Edition?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

My Operating System is Windows XP Prof SP2 and I had downloaded the latest version 2.11.15.0 from APC's website.. Thank You

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

You've uninstalled the software, and it still freezes? At this point, I would disconnect the USB communication cable and see if the problem still persists. I would also download Windows Defender and run a scan on your machine. It may not be the software that is causing the freeze.

Also, What are the specs on the PC? Specifically related to memory size? If you leave your computer running for weeks at a time, memory utilization can start to creep up.

Message was edited by: The Notorious K.M.P.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

I have an HP Media Center m7170n Computer running Windows XP Prof SP2 with 2 GB Ram, 3:00 Gigahertz Intel Pentium D, Maxtor 300 GB Hard Drive. I have McAfee Virus and Firewall, Spysweeper and Ad-Aware which I run every 2 Days. My Problem didn't start until I installed the UPS Battery backup Prior to that my Computer never froze. When You say unhook the USB Communication Cable I guess that You mean the cable running from the Data Port to one USB Outlet. If I unhook that, will I still have the battery Backup. In other words will the battery backup still take over when we loose the Power? If I need to disconnect it, I will. it is just that where i live, we loose our Power often. I check Event Viewer every time I freeze but their never is an entry with regard to the Freezing. Thank You for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

Yes, if you remove the data cable, the UPS will still transfer to battery upon power loss. That is the next logical step.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

Thank You. I will do that and get back to you at a later time. Since their is no specific time limit that the computer freezes, it might be a while. Thank You

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

I would like to ask an other question. What would it mean if after removing the USB Communication Cable my Computer doesn't freeze anymore? That would give me an idea on how to proceed. Thank You

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

I think we can cross that bridge once we get to it. This is another unique situation, which is rarely, if ever, seen. Therefore we can analyze what's going on once we've eliminated the OS and any other software installed as a problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

We have been having this same problem for quite a few months. Un-Plugging the USB cable from the computer does stop the freezing but then you can't use the software to monitor your battery. Currently we have to unplug the USB cable and then start the computer, then plugging the USB cable back in after it starts up. This is obviously a work around for now but is there any way we can fix this? We are running Windows 2000 SP4 on this particular workstation. Anything to try would be appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

Dave,

Have you tried to reinstall or update the USB drivers for the device? Are all the ports on the machine running at 2.0? Have you tried all the ports on the machine?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:19 AM

I'll check on those things and if there is anything I can try out of that I will and I'll get back to you.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:18 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:18 AM

Hello. Same issue here using an ES-550. This is on XP Pro SP-3 and PowerChute 2.0 (latest version from website). Shortly after I installed this, I noticed my computer started hanging. It seemed that this often happened during my nightly AVG anti-virus scan but it could have happened other times as well. With the computer frozen completely it is hard to say when it happened or what else was going on. I have since removed PowerChute and am using the native UPS support in XP. Since then, I have not had a single hang. This is not proof positive but strongly suggests there is some issue with PowerChute.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:18 AM

0 Likes
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:18 AM

Similar thing is happening here. I am using Vista 32 bits with PS 2.1.1. My pc started to freeze on every power drop (and we get a lot of small surges everyday), so I reinstalled my Vista. At first (after the clean install) it was working perfectly, but out of nowhere it started to freeze again. The strange thing is that it is not a complete freeze, the pc is just very very very slow... I mean, you move the mouse and the cursor will move after 4-5 minutes. I am still testing to find out if it is the APC data cable, or some other device attached to a USB port that may be loosing power whenever the power drops... but so far no luck. APC customer service was unable to help either. Now, I have the same APC model (RS1500) on three different computers (all with the same OS - Vista 32), but this is only happening to one of them.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:18 AM

0 Likes
0
3918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:24 PM . Last Modified: ‎2024-03-26 01:18 AM

I bought the Back-UPS BX1300 and I have been having Problems with the Computer freezing since. I have been in touch with the Support team and have uninstalled the Program that comes with it and downloaded the new version. Un installed that and I am still having the same Problem. My Computer freezes every so often It could be 2 Days or 2 Weeks in between. This has been going on now for two months. I don't know what to do or how to find out what is causing it. I would be so happy if someone could help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore