Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Cheapest Online / Double Conversion UPS ? (for a small server)

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Cheapest Online / Double Conversion UPS ? (for a small server)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:02 AM

0 Likes
11
3760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:02 AM

Cheapest Online / Double Conversion UPS ? (for a small server)

Hi.

I have a small server in a remote office that needs to be protected from power surges. Usually, this scenario is fulfilled by BackUPS, no problem - since it's just one small server.

However, this particular location turn out to suffer from (REALLY) bad power supply. The electric company in this area really sucks - the surges are very visible, each lasted for several seconds, and it happens 5 - 6 times daily.
I was surprised to find BackUPS not able to protect the server in this case. It was that bad.

So I looked around to find another suitable APC product - but got thoroughly confused instead πŸ™‚
But I think I'll need a UPS with a feature called "double conversion" / online UPS

However, I found it very difficult to find, for sure, which APC products with this feature. After googling and browsing around for 6 hours (God my eyes hurt!) I gave up, and turned to this forum. Hopefully somebody would be able to enlighten me.

My question: Which APC UPS product is the cheapest with online / double conversion feature ?

Thank you.


Regards,
Harry

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • cheapest
  • double_conversion
  • online
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkC_apc
Commander MarkC_apc
Commander

Posted: β€Ž2021-06-29 08:52 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:52 PM . Last Modified: β€Ž2024-03-20 06:01 AM

Not sure of protocols on this website and apologize if overstepping Schneider's intent, but you could likely find a waranteed, refurbished APC double conversion unit on ebay for the price range you are looking for.  I'm quite familiar with these units as I use  SURT6000/5000's with a Prius to generate 240 volt split phase power for my rural property in emergencies.  They are very robust units and have battery cages that are easily upgraded with all new batteries (very important to keep top quality batteries in the APC UPSs).  Be sure to get the proper WATTAGE with these units as their power factor is not always high (the new SRT line appears to be very good! - $$$s).   These are all "smart" units and can communicate in many, helpful ways.

Highly recommend one of these rather than a home built "battery/outlet" (IMO)  especially if you want a warning of impending disaster!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:02 AM

0 Likes
0
3758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:02 AM

Here you go:
http://www.apc.com/products/family/index.cfm?id=163

The Back UPS Range is normally (few exceptions like e.g. the RS) is Offline
Most Smart UPS are Line-interactive
And starting from the RT Range we go Online πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:02 AM

0 Likes
0
3758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:02 AM

Thanks ! πŸ˜„ That's about as clear as it can be.

Unfortunately, the RT series is beyond the budget for this project. The cheapest I could find is SURT1000XLI / Smart UPS RT XL 1000v, and it's priced around US$ 700.

For now I'll purchase Smart UPS 420VA, to better cover the server for the moment.
While making the proposal for the SURT1000XLI.

Thanks again for the summary. Much appreciated.


cheers,
Harry

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

The Smart UPS SC Range is basically pretty much the same as the Back UPS RS Range - except for the Business Edition Software coming with it.
I would recommend starting with an SUA750I if you really want to go with a Smart UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

Yes, the UPS Model number SUA750I will be the basic model in Smart UPS and cheapest only.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

The Smart-UPS SC 420 is a lot like a Back-UPS, it just has smart signaling. It'll give you basically the same exact protection the Back-UPS did. You might be better off with a "true" Smart-UPS, not something in the SC family.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

>
The Smart-UPS SC 420 is a lot like a Back-UPS, it just has smart signaling. It'll give you basically the same exact protection the Back-UPS did. You might be better off with a "true" Smart-UPS, not something in the SC family.

Any recommendations ?

Some of our remote offices have started to experience deteriorating power conditions - to the point where SC420i is no longer able to protect them. Some of the servers there have had data corruption incidents due to this.

I'm still unable to get my proposal for SURT1000XLI approved. While to my knowledge, that is THE cheapest true online UPS (*) from APC.

Do feel free to correct me if I'm wrong - if there's any online UPS in $ 300-400 range, I can get them approved quickly for these suffering remote offices.


Thanks!
Harry

(*) true online UPS : I'm thinking about a UPS where the devices connected to them will be fed with power straight from the UPS's battery, at ALL times.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

If you are looking for the cheapest Double Conversion Online UPS then you are correct, the [SURT1000XLI|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT1000XLI&total_watts=200] is the cheapest that you can get. The rack mountable version of it is [SURT1000RMXLI|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT1000RMXLI&total_watts=2...].

To know more about different UPS systems please see this APC Knowledge Base - [Different Types of UPS Systems|http://jpaa-en.apc.com/app/answers/detail/a_id/727/kw/topologies/session/L3RpbWUvMTMxMDIyMTMxNC9zaWQ...]

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

Jonathan, thanks for the confirmation.

Before you replied, I've also contacted a friend of mine who happen to be an electrician too. My future strategy would be to equip remote offices with APC SC420i, and the ones with nasty power supply will be provided with a custom-made UPS made by my friend (basically a sealed car battery with AC socket). Because we just need the power protection feature, that's all.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:51 PM . Last Modified: β€Ž2024-03-20 06:01 AM

Not a problem. I am glad that I was still able to help. I do hope that the solution would fix the problem that you're having on your remote offices.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
cogeanumarius_apc
cogeanumarius_apc
Cadet

Posted: β€Ž2021-06-29 08:52 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:52 PM . Last Modified: β€Ž2024-03-20 06:01 AM

I like the easy explanation,  but maybe it is not anymore valid, can we have an updated version of it?

As I can see today, we have "line interactive" description for all the Back-UPS range on latest models, like: APC Back-UPS 500/650/700/950/1400 BX, APC Power Saving Back-UPS Pro 550/900...and the list could continue, all these have no SMART in the name but all are "line interactive"

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
MarkC_apc
Commander MarkC_apc
Commander

Posted: β€Ž2021-06-29 08:52 PM . Last Modified: β€Ž2024-03-20 06:01 AM

0 Likes
0
3759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:52 PM . Last Modified: β€Ž2024-03-20 06:01 AM

Not sure of protocols on this website and apologize if overstepping Schneider's intent, but you could likely find a waranteed, refurbished APC double conversion unit on ebay for the price range you are looking for.  I'm quite familiar with these units as I use  SURT6000/5000's with a Prius to generate 240 volt split phase power for my rural property in emergencies.  They are very robust units and have battery cages that are easily upgraded with all new batteries (very important to keep top quality batteries in the APC UPSs).  Be sure to get the proper WATTAGE with these units as their power factor is not always high (the new SRT line appears to be very good! - $$$s).   These are all "smart" units and can communicate in many, helpful ways.

Highly recommend one of these rather than a home built "battery/outlet" (IMO)  especially if you want a warning of impending disaster!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of