Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:52 PM . Last Modified: 2024-03-20 06:00 AM
How would one provision for air distribution redundancy when designing a data center with in-row cooling? The problem that I am stuck with is if I have an in-row rc failure at either end of the row, how does cool air now get to those racks?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:52 PM . Last Modified: 2024-03-20 06:00 AM
no HACS. Having redundant RCs at either end, as you have shown looks like a feasible way to do it.
Any thoughts on using a perimeter downflow crac unit with perf panels that have slide dampers to control air flow distribution for backing up my RC's?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:52 PM . Last Modified: 2024-03-20 06:00 AM
You can build additional RC's into the solution. IE
RACK | RC | RC | RACK | RACK | RC | RC | RACK
RACK | RC | RC | RACK | RACK | RC | RC | RACK
Would you be building these RC's into a enclosed Hotaisle?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:52 PM . Last Modified: 2024-03-20 06:00 AM
no HACS. Having redundant RCs at either end, as you have shown looks like a feasible way to do it.
Any thoughts on using a perimeter downflow crac unit with perf panels that have slide dampers to control air flow distribution for backing up my RC's?