Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:52 PM . Last Modified: 2024-03-20 06:00 AM
How would one provision for air distribution redundancy when designing a data center with in-row cooling? The problem that I am stuck with is if I have an in-row rc failure at either end of the row, how does cool air now get to those racks?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:52 PM . Last Modified: 2024-03-20 06:00 AM
no HACS. Having redundant RCs at either end, as you have shown looks like a feasible way to do it.
Any thoughts on using a perimeter downflow crac unit with perf panels that have slide dampers to control air flow distribution for backing up my RC's?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:52 PM . Last Modified: 2024-03-20 06:00 AM
You can build additional RC's into the solution. IE
RACK | RC | RC | RACK | RACK | RC | RC | RACK
RACK | RC | RC | RACK | RACK | RC | RC | RACK
Would you be building these RC's into a enclosed Hotaisle?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:52 PM . Last Modified: 2024-03-20 06:00 AM
no HACS. Having redundant RCs at either end, as you have shown looks like a feasible way to do it.
Any thoughts on using a perimeter downflow crac unit with perf panels that have slide dampers to control air flow distribution for backing up my RC's?
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.