Can the bypass switch be extended off my SURT10000RMX6U for easier access?

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
john_a__apc
Cadet
0 Likes
1
129

Can the bypass switch be extended off my SURT10000RMX6U for easier access?

This was originally posted on APC forums on 9/11/2013


I have a rack mount unit in a data closet that is very difficult to reach. It is at a remote site, so there is a very good possibility that I will be talking some non-technical person through the process of changing to bypass over the phone. The switch seems to be integrated in the device, not part of a replaceable module.


Is there any way for me to extend this switch to a more convenient  location in the front of the cabinet?


Thanks in advance for any insight you have for me.


-John Aitchison


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
129

Re: Can the bypass switch be extended off my SURT10000RMX6U for easier access?

This reply was originally posted by Angela on APC forums on 9/11/2013


This UPS has a logical bypass versus a mechanical bypass just as an FYI. For accessing the bypass on the UPS itself, you could consider a UPS Network Management Card for remote access to the UPS to command it in and out of bypass. Also an option is the ability to command it in and out of bypass using dry contacts with the AP9613. One of the AP9613 inputs allows you to command the unit in and out of bypass which you could also wire to a switch some place near the front of the closet.

If you had a wrap around service bypass panel, these are a separate module that allow you to mechanically bypass the UPS completely and have a big knob on the front.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
130

Re: Can the bypass switch be extended off my SURT10000RMX6U for easier access?

This reply was originally posted by Angela on APC forums on 9/11/2013


This UPS has a logical bypass versus a mechanical bypass just as an FYI. For accessing the bypass on the UPS itself, you could consider a UPS Network Management Card for remote access to the UPS to command it in and out of bypass. Also an option is the ability to command it in and out of bypass using dry contacts with the AP9613. One of the AP9613 inputs allows you to command the unit in and out of bypass which you could also wire to a switch some place near the front of the closet.

If you had a wrap around service bypass panel, these are a separate module that allow you to mechanically bypass the UPS completely and have a big knob on the front.