Blown fuse for battery - XS 1500

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Blown fuse for battery - XS 1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

0 Likes
4
6860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

Blown fuse for battery - XS 1500

Fuse on main board of Back-UPS XS 1500. I've blown the two fuses on the main board of my UPS. I was using an external battery that had a wiring short. The UPS will turn on but the battery will not connect because of the blown fuse.

I thought it was a simple automotive blade type fuse - marked 30 on the top. But after I removed the fuse - it was not automotive. The legs of the fuse are attached to the main board and the plastic top comes off.

Anyway - even worse. The fuse part (part that blows) is attached to the legs and is permanently on the board. I guess these type of fuses are not to be removed and replaced.

This is the fuse for the battery input wires - not the 110v cord breaker button thingy.

Fuse is marked Littel Fuse 30 32V 257. I looked it up and the web page shows an automotive blade type fuse. That is not what is there. The legs are soldered to the board. I have the plastic green tops in my hand how.

Any ideas??

attached pic is example - not my UPS

Attachments
Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

0 Likes
0
6857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

That's exactly what it looks like. The blade type fuse and APC just soldered to the PCB.

Now will soldering it mess up the fuseable part of it?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

0 Likes
0
6857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

Thanks for your help. I've decided that APC did a very strange thing and took regular blade automotive fuses and yes - soldered the legs directly to the PCB. Strange when there are many other types of mounted fuse types they could have chosen so that they can could have been easily replaced.

Got to heat up my gun now. I've read it takes a lot of heat to melt the fuseable link part anyway. Like over 1,000F.

Message was edited by: eric512

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

That's exactly what it looks like. The blade type fuse and APC just soldered to the PCB.

Now will soldering it mess up the fuseable part of it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

Thanks for your help. I've decided that APC did a very strange thing and took regular blade automotive fuses and yes - soldered the legs directly to the PCB. Strange when there are many other types of mounted fuse types they could have chosen so that they can could have been easily replaced.

Got to heat up my gun now. I've read it takes a lot of heat to melt the fuseable link part anyway. Like over 1,000F.

Message was edited by: eric512

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

0 Likes
0
6857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

>
Fuse is marked Littel Fuse 30 32V 257. I looked it up and the web page shows an automotive blade type fuse. That is not what is there. The legs are soldered to the board. I have the plastic green tops in my hand how.

Any ideas??
>

The picture you attached looks like the picture of the blade type fuse (as marked) on Littel's website: http://www.littelfuse.com/data/en/Data_Sheets/Littelfuse_BladeFuse_ATO32V.pdf

Perhaps they take one of those and solder the legs to the PCB?

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

0 Likes
0
6857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

Well you only really face one option.. You have two blown fuses that are soldiered onto the PCA. The only way to find out if you can soldier them on without blowing them is to do it. I'd order a couple extra just in case you mess one up. As it stands your circuit is broken so by not soldering the new fuses in it will remain broken. I don't believe your going to find anyone hear that will say "go ahead and soldier them on, your not going to damage anything else"


Good luck!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore