Blown fuse for battery - XS 1500

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
Enter a search word
    Turn off suggestions

    Didn't find what you were looking for? Explore advanced search

    Enter a search word
      Turn off suggestions

      Didn't find what you were looking for? Explore advanced search

      Enter a user name or rank
        Turn off suggestions

        Didn't find what you were looking for? Explore advanced search

        Enter a search word
          Turn off suggestions

          Didn't find what you were looking for? Explore advanced search

          Enter a search word
            Turn off suggestions

            Didn't find what you were looking for? Explore advanced search

            cancel
            Turn on suggestions
            Showing results for 
            Show  only  | Search instead for 
            Did you mean: 
            Important Note
            • Home
            • Schneider Electric Community
            • APC UPS, Critical Power, Cooling and Racks
            • APC UPS for Home and Office Forum
            • Re: Blown fuse for battery - XS 1500
            Options
            • Mark Topic as New
            • Mark Topic as Read
            • Float this Topic for Current User
            • Bookmark
            • Subscribe
            • Mute
            • Printer Friendly Page
            Invite a Co-worker
            Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
            You have entered an invalid email address. Please re-enter the email address.
            This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
            Please enter email address
            Send Invite Cancel
            Invitation Sent
            Your invitation was sent.Thanks for sharing Exchange with your co-worker.
            Send New Invite Close
            Top Experts
            User Count
            BillP
            Administrator BillP Administrator
            2151
            Teken
            Spock Teken
            110
            voidstar_apc
            Janeway voidstar_apc
            83
            View All

            Invite a Colleague

            Found this content useful? Share it with a Colleague!

            Invite a Colleague Invite
            Solved Go to Solution
            Back to APC UPS for Home and Office Forum
            Start a Topic
            Solved
            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

            0 Likes
            4
            6678
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

            Blown fuse for battery - XS 1500

            Fuse on main board of Back-UPS XS 1500. I've blown the two fuses on the main board of my UPS. I was using an external battery that had a wiring short. The UPS will turn on but the battery will not connect because of the blown fuse.

            I thought it was a simple automotive blade type fuse - marked 30 on the top. But after I removed the fuse - it was not automotive. The legs of the fuse are attached to the main board and the plastic top comes off.

            Anyway - even worse. The fuse part (part that blows) is attached to the legs and is permanently on the board. I guess these type of fuses are not to be removed and replaced.

            This is the fuse for the battery input wires - not the 110v cord breaker button thingy.

            Fuse is marked Littel Fuse 30 32V 257. I looked it up and the web page shows an automotive blade type fuse. That is not what is there. The legs are soldered to the board. I have the plastic green tops in my hand how.

            Any ideas??

            attached pic is example - not my UPS

            Attachments
            257 mount (800x600).jpg
            Labels
            • Labels:
            • Back-UPS & Surge Protectors
            Reply

            Link copied. Please paste this link to share this article on your social media post.

            • All forum topics
            • Previous Topic
            • Next Topic

            Accepted Solutions
            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

            0 Likes
            0
            6675
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

            That's exactly what it looks like. The blade type fuse and APC just soldered to the PCB.

            Now will soldering it mess up the fuseable part of it?

            See Answer In Context

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

            0 Likes
            0
            6675
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

            Thanks for your help. I've decided that APC did a very strange thing and took regular blade automotive fuses and yes - soldered the legs directly to the PCB. Strange when there are many other types of mounted fuse types they could have chosen so that they can could have been easily replaced.

            Got to heat up my gun now. I've read it takes a lot of heat to melt the fuseable link part anyway. Like over 1,000F.

            Message was edited by: eric512

            See Answer In Context

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Replies 4
            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

            0 Likes
            0
            6676
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-22 12:23 AM

            That's exactly what it looks like. The blade type fuse and APC just soldered to the PCB.

            Now will soldering it mess up the fuseable part of it?

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

            0 Likes
            0
            6676
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

            Thanks for your help. I've decided that APC did a very strange thing and took regular blade automotive fuses and yes - soldered the legs directly to the PCB. Strange when there are many other types of mounted fuse types they could have chosen so that they can could have been easily replaced.

            Got to heat up my gun now. I've read it takes a lot of heat to melt the fuseable link part anyway. Like over 1,000F.

            Message was edited by: eric512

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            voidstar_apc
            Janeway voidstar_apc
            Janeway

            Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

            0 Likes
            0
            6675
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

            >
            Fuse is marked Littel Fuse 30 32V 257. I looked it up and the web page shows an automotive blade type fuse. That is not what is there. The legs are soldered to the board. I have the plastic green tops in my hand how.

            Any ideas??
            >

            The picture you attached looks like the picture of the blade type fuse (as marked) on Littel's website: http://www.littelfuse.com/data/en/Data_Sheets/Littelfuse_BladeFuse_ATO32V.pdf

            Perhaps they take one of those and solder the legs to the PCB?

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            upsguy_apc
            Commander upsguy_apc
            Commander

            Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

            0 Likes
            0
            6675
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 04:53 AM . Last Modified: ‎2024-03-22 12:23 AM

            Well you only really face one option.. You have two blown fuses that are soldiered onto the PCA. The only way to find out if you can soldier them on without blowing them is to do it. I'd order a couple extra just in case you mess one up. As it stands your circuit is broken so by not soldering the new fuses in it will remain broken. I don't believe your going to find anyone hear that will say "go ahead and soldier them on, your not going to damage anything else"


            Good luck!

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Preview Exit Preview

            Photos

            • Upload Upload
            • URL URL
            • Saved Photos Saved Photos
            Upload location
            • Add Photos to Album:
            • New Album
            • Upload location
              • Add Photos to Album:
              • New Album
              Drag here to start uploading
              Drag photos here or
              Tap for upload options
              You must install or upgrade to the latest version of Adobe Flash Player before you can upload images.
            Photos

            never-displayed

            You must be signed in to add attachments

            never-displayed

             

            You’ve reached the end of your document

            WHAT’S NEXT?

            Ask our Experts

            Didn't find what you are looking for? Ask our experts!

            My Dashboard

            Check out the new Feeds and activities that are relevant to you.

            To The Top!

            Forums

            • APC UPS Data Center Backup Solutions
            • EcoStruxure IT
            • EcoStruxure Geo SCADA Expert
            • Metering & Power Quality
            • Schneider Electric Wiser

            Knowledge Center

            Events & webinars

            Ideas

            Blogs

            Get Started

            • Ask the Community
            • Community Guidelines
            • Community User Guide
            • How-To & Best Practice
            • Experts Leaderboard
            • Contact Support
            Brand-Logo
            Welcome to Schneider Electric Community!
            Forum-Icon

            You have two options to continue your visit.

            LOGIN / Register

            Why logging in?
            • You enable the complete set of features available, such as posting, sharing, subscribing, private messaging and more.
            • You unlock the access to the whole content that Schneider Electric Community has to offer, including the gated items and the special events.
            And it’s free of charge!!!

            OR

            Continue as a guest

            Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

            Welcome!

            Welcome to your new personalized space.

            of 1

            Explore
            Translating the page…
            The page is currently translating. Please wait.
            Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.