Last week i had a power cut in my house, i got around 15 minutes Backup from my APC Back-UPS RS 1100. After a couple of days i had another power cut in which all of d sudden my UPS starts Beeping like it has no backup and shutdowns immediately. Even this happened yesterday, it only lasts for 5 seconds there's no way for me to shutdown my PC.
My UPS is only connected with Monitor & CPU (PSU 550).
Thanks in Advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:03 PM . Last Modified: 2024-03-20 03:22 AM
Hi,
If the UPS is shutting down that quickly and the load is light the battery may need to be replaced. Have you run a self-test and does to pass? You can run a manual self-test by holding in the power on button for 10 seconds. You can also test the battery by removing the computer and monitor and plugging a lamp into the UPS. Remove AC power to the UPS and monitor to see how long the lamp stays lit.
Batteries are warrantied for 2 years so if the unit is less that 2 years old or the battery is less the 2 years old you should contact local technical support for assistance.
If the battery is greater then 2 years old and if fails during testing you can purchase a replacement at apc.com.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:03 PM . Last Modified: 2024-03-20 03:22 AM
Hi,
If the UPS is shutting down that quickly and the load is light the battery may need to be replaced. Have you run a self-test and does to pass? You can run a manual self-test by holding in the power on button for 10 seconds. You can also test the battery by removing the computer and monitor and plugging a lamp into the UPS. Remove AC power to the UPS and monitor to see how long the lamp stays lit.
Batteries are warrantied for 2 years so if the unit is less that 2 years old or the battery is less the 2 years old you should contact local technical support for assistance.
If the battery is greater then 2 years old and if fails during testing you can purchase a replacement at apc.com.