Back UPS cs 650 - Power to "Surge Protect" outlet but no power to the "Battery Backup" power outlets

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back UPS cs 650 - Power to "Surge Protect" outlet but no power to the "Battery Backup" power outlets
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:39 AM

0 Likes
3
2910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:39 AM

Back UPS cs 650 - Power to "Surge Protect" outlet but no power to the "Battery Backup" power outlets

As in the title I have a Back UPS CS 650 and its been out of service for a while, so I replaced the battery and;

-it fires up fine with a new battery

-Solid Green Power Light

-Self test in Power Chute PASSES without note

-In powerchute indicates battery is full and AC supply is 258V

-Surge Protected outlet has power - 255V (multimeter)

-Battery Backup outlets (all 3) have 0.00 voltage (multimeter)

-Battery cables from unit unplugged from battery - 13.5V

-Battery Cables plugged into battery - 12.5V

Not sure what other info I can provide, but not sure why I can't seem to get power through the battery. Tried a second battery (not brand new but not dead) and got the exact same results, on battery voltage was 12.0 on the older battery.

Am I missing something obvious or is there a fault in this unit somewhere?

Thanks in advance for anyone who has time to comment.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:38 AM

0 Likes
0
2909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:38 AM

Before I get to anything else, please be aware that these units are dangerous to work on. If you don't have the knowledge to safely repair high power electronic devices, the only safe option is to replace the unit. I'm deadly serious: these units can kill a person if they don't understand what's going on inside. They are considered to be non-repairable by APC.

All of that said, the relay is inside the unit, mounted to the main printed circuit board. It is soldered in place. One would have to diagnose not only the relay's driving circuit (is it outputting enough voltage to close the relay's contacts?) and the relay itself (which could have developed burned contacts or simply failed in some other way). Bad solder joints are not unheard of.

Your electrician might have knowledge sufficient to investigate and repair the problem, although you really want someone skilled in electronics repair. Of course, if you find someone willing to work on the unit, it may cost as much as a new one to have it fixed. Another problem is that of schematics not being readily available for these units.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:39 AM

0 Likes
0
2909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:39 AM

Hi,

If you cold start the UPS (start from battery not AC) is power passed to the outlets? If that is the case it could be a bad relay. If not it is most likely a bad connection. The unit is not considered user repairable but the test should help you understand the possible cause. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:38 AM

0 Likes
0
2909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:38 AM

It does fire up fine with no AC and power the battery backup points.

Where would i find the offending relay?

I'll have our electrician electrician check it out.

Thanks for taking the time to reply, its much appreciated.

Josh

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:38 AM

0 Likes
0
2910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-27 01:38 AM

Before I get to anything else, please be aware that these units are dangerous to work on. If you don't have the knowledge to safely repair high power electronic devices, the only safe option is to replace the unit. I'm deadly serious: these units can kill a person if they don't understand what's going on inside. They are considered to be non-repairable by APC.

All of that said, the relay is inside the unit, mounted to the main printed circuit board. It is soldered in place. One would have to diagnose not only the relay's driving circuit (is it outputting enough voltage to close the relay's contacts?) and the relay itself (which could have developed burned contacts or simply failed in some other way). Bad solder joints are not unheard of.

Your electrician might have knowledge sufficient to investigate and repair the problem, although you really want someone skilled in electronics repair. Of course, if you find someone willing to work on the unit, it may cost as much as a new one to have it fixed. Another problem is that of schematics not being readily available for these units.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore