Back-UPS XS 900 BX900R Overload Light

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS XS 900 BX900R Overload Light
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:47 AM

0 Likes
4
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:47 AM

Back-UPS XS 900 BX900R Overload Light

According to the software this thing was way underloaded and worked well for about a year but now it'll cut off my computer and monitor and flash the overload light. The computer and monitor combined under load pulled only 134 watts so i can't understand why this thing is overloaded. Any ideas? Back-UPS XS 900 BX900R Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:46 AM

0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:46 AM

We had 4 of these units and all 4 units went to overload alarm within two weeks of each outher.  They were bought and put inservice on the same day.  All of the units have had the same load on theme from the day they were installed.  

Not that I know for sure but it sounds like there is a timer circuit on the main board the makes them fail after a period of time.  It just look way to coincidental with 4 different units failing all within a week.  I for one are seeking alternative to Schneider Group offerings

See Answer In Context

  • Tags:
  • 4
  • 4_failed_Units
  • failed
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:47 AM

0 Likes
0
1211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:47 AM

If you attempt a cold start, does it go immediately into overload?

To cold start:
1. Unplug UPS from wall (while it's off)
2. Disconnect attached load
3. Depress power button
4. Continue to hold power button and release during the second, longer beep

This will force the UPS on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:47 AM

0 Likes
0
1211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:47 AM

I tried that, ran it until it almost died, then plugged everything as usual and it the overload light comes on again. Ran fine on battery. Couldn't even leave it plugged in long enough to fully charge, even with nothing plugged into it.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:47 AM

0 Likes
0
1211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:47 AM

If it's covered, I'd give tech support a call and get it replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:46 AM

0 Likes
0
1211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:03 PM . Last Modified: ‎2024-03-26 12:46 AM

We had 4 of these units and all 4 units went to overload alarm within two weeks of each outher.  They were bought and put inservice on the same day.  All of the units have had the same load on theme from the day they were installed.  

Not that I know for sure but it sounds like there is a timer circuit on the main board the makes them fail after a period of time.  It just look way to coincidental with 4 different units failing all within a week.  I for one are seeking alternative to Schneider Group offerings

  • Tags:
  • 4
  • 4_failed_Units
  • failed
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore