Back-UPS XS 1300 LCD has strangely low runtime even with new battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS XS 1300 LCD has strangely low runtime even with new battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
rseiler_apc
Ensign rseiler_apc
Ensign

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-21 05:47 AM

0 Likes
3
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 AM . Last Modified: ‎2024-03-21 05:47 AM

Back-UPS XS 1300 LCD has strangely low runtime even with new battery

This BX1300LCD has me puzzled. Despite a load that varies between about 190W and 230W (two PCs, a modem, a router, no monitors, no printers), the runtime is about 12-15 mins. That's about a 25% load, so the runtime should be MUCH higher.

The first battery was about 3 years old, so recently I replaced it even though a self-test passed (I don't recall what the runtime used to be years ago, unfortunately). However, nothing has changed with the new battery despite the fact that it's now 100% charged. The above numbers on the LCD panel agree with PowerChute.

Getting another battery isn't practical, and the odds of two batteries having the exact same problem are vanishingly low, so what else can I check?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
rseiler_apc
Ensign rseiler_apc
Ensign

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-21 05:46 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-21 05:46 AM

Online (and PowerChute says "AC Utility Power").

I'll try that at the next opportunity. I noticed yesterday that there was an approx 90-second outage and that it survived that well, but it sounds like you're thinking that the numbers might not be accurate and that it could go well over 15 mins (like it should).

If this is the problem, is there such a thing as "resetting" a UPS to sync it back with reality?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-21 05:47 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-21 05:47 AM

Hi Rseiler,

Sorry for the late reply.

You might want to try to see the actual runtime when you switch the UPS to on battery state.

Actually, we have another procedure for runtime issue but right now, it's too ealy to do that specific procedure.

Please let us know the outcome.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-21 05:46 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-21 05:46 AM

Hi rseiler,

Good day!

What is the state of the UPS (on line or on battery) when you see 12-15mins?

Try unplugging the UPS from the wall while the loads are pulling power from the UPS, see how much runtime it'll record.

Reply

Link copied. Please paste this link to share this article on your social media post.

rseiler_apc
Ensign rseiler_apc
Ensign

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-21 05:46 AM

0 Likes
0
1944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:07 AM . Last Modified: ‎2024-03-21 05:46 AM

Online (and PowerChute says "AC Utility Power").

I'll try that at the next opportunity. I noticed yesterday that there was an approx 90-second outage and that it survived that well, but it sounds like you're thinking that the numbers might not be accurate and that it could go well over 15 mins (like it should).

If this is the problem, is there such a thing as "resetting" a UPS to sync it back with reality?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore