Back UPS 750 constant beeping/new battery?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back UPS 750 constant beeping/new battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
124
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-21 05:24 AM

0 Likes
4
9714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-21 05:24 AM

Back UPS 750 constant beeping/new battery?

I have a Back UPS 750 that's a few years old. I got a constant beeping from the unit when turned on, so I figured I needed to replace the battery. Got a new battery, plugged the unit it to let it charge, turned the UPS on, still a constant beeping.

Any suggestions? Is the UPS just bad and I need a new one?

thanks,

Baird

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-21 05:24 AM

0 Likes
0
9710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-21 05:24 AM

So if the unit works fine but just the constant beep stays on? Does the constant beep goes off after a while or does it stay on? I have the SUA1500 server unit and after I put in a new battery, this problem occurs. Every thing works fine and this constant/whistling sound stay on and never go off. I wonder why? The internal fault is when you have all lights go on red and constant beeping sound. My USP unit works perfect except for that annoying constant beep.
Any ideas?
Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-21 05:23 AM

0 Likes
0
9710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-21 05:23 AM

Well, this is very odd, I just powered up the system to test what LEDs were blinking. The main power LED blinked green for several sec, and then the LED went out and the constant tone started. I turned the UPS off, then got a stopwatch to actually time the blinking. When I powered the system back on, the power LED blinked green for about 20 sec, there was a click, and the blinking stopped and the UPS seems to be functioning normally. There was absolutely nothing different about the situation now compared to the past. But it apparently works, so I guess that's the main point.

The white sticker on the back reads BEG750G and 3B0824X34168.

thanks,

Baird

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-21 05:24 AM

0 Likes
0
9711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-21 05:24 AM

So if the unit works fine but just the constant beep stays on? Does the constant beep goes off after a while or does it stay on? I have the SUA1500 server unit and after I put in a new battery, this problem occurs. Every thing works fine and this constant/whistling sound stay on and never go off. I wonder why? The internal fault is when you have all lights go on red and constant beeping sound. My USP unit works perfect except for that annoying constant beep.
Any ideas?
Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-21 05:23 AM

0 Likes
0
9710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:33 AM . Last Modified: ‎2024-03-21 05:23 AM

Baird,

Would you happen to have the exact model number of the UPS? This is usually located underneath the BackUPS, it is on a small white barcoded sticker. Aside from the constant beep, are you seeing any solid or flashing LEDs? If you do can you tell us exactly what color and icon is it on? These audible and visual indicators would help us determine the fault state of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-21 05:23 AM

0 Likes
0
9711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-21 05:23 AM

Well, this is very odd, I just powered up the system to test what LEDs were blinking. The main power LED blinked green for several sec, and then the LED went out and the constant tone started. I turned the UPS off, then got a stopwatch to actually time the blinking. When I powered the system back on, the power LED blinked green for about 20 sec, there was a click, and the blinking stopped and the UPS seems to be functioning normally. There was absolutely nothing different about the situation now compared to the past. But it apparently works, so I guess that's the main point.

The white sticker on the back reads BEG750G and 3B0824X34168.

thanks,

Baird

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-21 05:23 AM

0 Likes
0
9710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:34 AM . Last Modified: ‎2024-03-21 05:23 AM

When you turn the UPS on it goes to a cycle known as self-test. The UPS runs this diagnostic to check if there's something wrong with the battery. The click that you've heard comes from the relay inside the UPS especially if you have the Master Control function enabled.

For now, I do suggest that you keep an eye on this UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login