BX1300LCD - No Low Battery indicator but very low runtime

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BX1300LCD - No Low Battery indicator but very low runtime
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
rseiler_apc
Ensign rseiler_apc
Ensign

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

0 Likes
7
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

BX1300LCD - No Low Battery indicator but very low runtime

This is a 7 year-old UPS, so the warranty is long done. It's not on its first battery, but I don't know the history of it beyond the battery being installed about 2 years ago.

What's happening: with a 225W load (confirmed in Powerchute and LCD), the runtime is about 5 mins (100% charge). It should be more like 30.

If it's the battery, shouldn't the unit have the Low Battery indicator lit?  Powerchute doesn't see anything wrong either. Self-tests pass.

If it's not the battery, what could it be?  Could a UPS fail in this way?

Incidentally, the 5 mins figure is very real: it shuts off in that amount of time. It's not a case of the estimate being wrong.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • battery
  • bx1300lcd
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:46 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:46 AM

You're welcome

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

Hello,

i was recently helping the user in this thread (Re: New UPS "BR900GI" suddenly runtime is very low ) but it seems to be essentially the same issue and likely resolution. The only difference is you should validate the 5 minutes with no USB cable attached. Low battery indicator is a little different and you see it when the UPS is operating on battery and running low on capacity. Depending on UPS model, when you have low runtime and are online, you will get an indicator but I don't know if this one does that.

This is likely due to an aging battery and not the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

rseiler_apc
Ensign rseiler_apc
Ensign

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

Thanks, I didn't realize but should have that the low battery indicator measured battery capacity remaining during an outage.

About the cable, while I didn't disconnect it earlier, I did bring the PC out of Windows and into the BIOS during the last test. This way, when I pulled the plug on the UPS, Powerchute would have no effect, and when the PC suddenly lost power I wouldn't damage anything. That should be essentially the same as not having the cable plugged in, right?

One big difference with that other thread is that his runtime drop started suddenly. Mine is not sudden. I haven't been involved with this UPS for that long, but for at least a year it's been like this. I don't know if that changes the equation at all.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

Hi again,

I tend to agree with your thought on the USB cable but I can't say for sure if this particular UPS model does anything differently if it sees something active on the USB port (without further testing).

Do you know how old the battery is? If it reports 5 minutes but only really lasts 5 minutes without any outside software intervention, I still think it would be due to diminished capacity/life on the battery itself and not UPS related.

Reply

Link copied. Please paste this link to share this article on your social media post.

rseiler_apc
Ensign rseiler_apc
Ensign

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

The thing with many batteries is that you don't know how old they are when you get them, but I did some checking and this one was installed 3 years ago. At the time, its runtime was about 14 mins (same load), so it might have been a weak battery to start.

However, messages from that time also indicate that the runtime of the battery it replaced was ALSO 14 mins. That low number was in fact why they changed the battery in the first place.

It seems rather strange.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:47 AM

Yes, you should get about 33 minutes or so with a 225 watt load as you suggested. I agree it seems strange but I cannot say I have seen something like this be the fault of the UPS itself, like I said, unless PowerChute or a data connection to the UPS has caused an early shutdown to occur. That would not affect the displayed runtime though being 5 minutes too.

Do you know if the first battery replaced was the original? I would assume so based on when these model units were first released and how you said it was about 7 years old. And if the second battery was a genuine APC replacement battery?

My gut tells me the problem is with the battery capacity/useful life. Anywhere from 2-5 years is normal but not getting the full 33 minutes or so could be due to a poor quality battery from the start. Another suggestion to at least consider is since the UPS is older now, you could trade it in (with poor quality battery and all) to get a discount on a newer UPS with new battery and a 3 year warranty on both - rather than buying a new battery for the aging UPS.

Let me know if you have further questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

rseiler_apc
Ensign rseiler_apc
Ensign

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:46 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:46 AM

The latest battery wasn't genuine APC, but the previous battery likely was, as it was most likely the original (though I'm not sure).

OK, so at this point we'll decide between a known-good battery, the trade-in program, or some other UPS. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:46 AM

0 Likes
0
1900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:49 PM . Last Modified: ‎2024-03-20 03:46 AM

You're welcome

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore