IO Module status indicates Low Power Mode

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • IO Module status indicates Low Power Mode
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1621 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

IO Module status indicates Low Power Mode

Picard Product_Support
‎2018-09-06 10:03 AM

Issue

The IO Module does not report input signals and all physical outputs are turned off.

The IO module status LED blinks at a rate of one blink per second.

Product Line

EcoStruxure Building Operation

Environment

I/O Module

Cause

The IO module has been placed into Low Power Mode.

Resolution

 I/O Module Low Power Mode

In order to save energy, an I/O module can be placed in low power. When an I/O module is in low power, the following conditions apply:

  • The I/O module does not report input signals and all physical outputs are turned off.
  • The Module status reports low power.
  • The I/O module's LED pattern indicates low power (the slowest green LED blink pattern, approximately once every 3 seconds).

When you set an I/O module to low power, the software turns off all outputs.

When you want to recover an I/O module from low power, there are several points to consider:

  • Make sure all I/O module Output values are set to a safe level before a return to normal power conditions. This prevents "power surge" conditions.
  • After normal power resumes, the Output values set are reached immediately after any timing delay occurs.

Setting and Recovering an I/O Module from Low Power

Place an I/O module in low power mode in order to save energy and then recover that module later.  

To set and recover an I/O module from low power

  1. In WorkStation, in the System Tree pane, expand the IO Bus.
  2. Click the I/O module that you want to put in Low power mode.
  3. Click File and then Properties.
  4. Under Configuration Settings, in the Low power box, select True.
  5. Click OK to change the value and close the Properties tab.

If the physical I/O module, shown in the System Hardware folder, matches the logical I/O module defined in the I/O Bus, the I/O module goes into Low power.

After the physical module enters low power, the Module status attribute in the Status Information area displays Low power.

 To set and recover an I/O module from low power

  1. In the System Tree pane, expand the IO Bus to recover from low power mode.
  2. Click the I/O module to recover.
  3. Click File and then Properties.
  4. Under Configuration Settings, in the Low power box, select False.
  5. Click OK to change the value and close the Properties pane.

If the physical I/O module, shown in the System Hardware folder, matches the logical I/O module defined in the I/O Bus folder, the I/O module exits from low power.

After the module resumes operation from low power, the Module status returns to the status it had before it went into Low power.

NOTE: If unable to change the Low Power property:

  1. Export the contents of the I/O module
  2. Deleted it from the AS
  3. Re-add it to the AS
  4. Import the XML back into the module
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 14416
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore