Low Battery Duration and true runtime remaining

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Low Battery Duration and true runtime remaining
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
10
2547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Low Battery Duration and true runtime remaining

Hello,

I want to get the maximum battery runtime on the SmartUPS 1400 and I am attempting to understand how the settings in the management card affect when the low battery signal is sent to the clients.

If I set the Low Battery Duration to 2 minutes and the Shutdown Delay to 20 seconds and the Maximum Required Delay is 2 minutes, when does the UPS actually send the low battery signal? With 2 minues left? 4 minues left? 4:20 left?

If I increase the Shutdown delay to 180 seconds, does this cause the low battery signal to be sent 160 seconds sooner? What if I increase the PowerChust command runtime to say 300 seconds so tha the Maximum Required Delay is then 6 minues. Does this cause the low battery signal to then come 4 minutes sooner? This is all very poorly documented.

Any help appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • network_management_card
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:25 AM . Last Modified: ‎2024-03-08 12:10 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:25 AM . Last Modified: ‎2024-03-08 12:10 AM

Hello,

I want to get the maximum battery runtime on the SmartUPS 1400 and I am attempting to understand how the settings in the management card affect when the low battery signal is sent to the clients.

If I set the Low Battery Duration to 2 minutes and the Shutdown Delay to 20 seconds and the Maximum Required Delay is 2 minutes, when does the UPS actually send the low battery signal? With 2 minues left? 4 minues left? 4:20 left?

If I increase the Shutdown delay to 180 seconds, does this cause the low battery signal to be sent 160 seconds sooner? What if I increase the PowerChust command runtime to say 300 seconds so tha the Maximum Required Delay is then 6 minues. Does this cause the low battery signal to then come 4 minutes sooner? This is all very poorly documented.

Any help appreciated.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Thanks for your repsonse, but it's not clear, no. If the "Low Battery Duration" is 5 minutes, does this really mean that there are five minutes left on the battery? If that's true, where's the power to operate during the "Shutdown Delay?" Is the Shutdown Delay included in the Low Battery Duration? Also what about the "Two extra minutes to allow for unforeseen circumstances" discussed in the help file. Is that added to the "Low Battery Duration" or is it included in it?

I don't see a setting for "minutes on backup power" in the Management Card.

Thanks again.

Message was edited by: aurelius

Message was edited by: aurelius

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Hello,

The Total Time Required for Shutdown (which is the only number that should have attention paid to it) is the following:

Low Battery Signal Time + Shutdown Delay + (If configured, Maxmimum required delay). Maxmimum required delay takes the longest time from all configured PCNS clients to shutdown, and reports that time back to the card if you use "Force Negotiation" .

As for the "on battery after X minutes" that KVar was referring to, this is PER CLIENT in the PCNS Web Interface. When you select an event to shut down a server, it will go to a screen with a check box saying "Yes, I want to shutdown the server" then the next line will say "only after event has lasted this long (seconds)". This works well if you have servers that are more mission critical than others, and need them to shutodown last. That way you can have a server shutdown, then your Exchange server (if applicable), in case the first server needs to send an email, or finish a task that utilizes exchange.

I hope that was made clear, I apologize if it wasn't.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Hello,

By "Low Battery Signal Time" I assume that you mean "Low Battery Duration."

I thought that the Maximum Required Delay was an alternative to the Low Battery Duration. I.e., the card uses whichever one is greater. Is this not the case?

I'm not configuring anything on the clients yet. I'm just trying to understand the settings on the UPS.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

From the help file:

Shutdown Delay Defines how long the UPS waits before it shuts down in response to a turn-off command.

Therefore, if you have PCNS installed, or PCBE, if the UPS is told to turn off AFTER the shutdown is complete, it will wait that amount of time before shutting down after receiving that message.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

That's not what happens. Try setting your Low Battery Duration to 10 minutes and your Shutdown Delay for 20 seconds. The The servers will shutdown but the UPS will stay on for at least 10 minutes.

Actaully, it seems like 10 minues + 2 minutes + 20 seconds, but I'm not sure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

aurelius wrote:
Hello,

By "Low Battery Signal Time" I assume that you mean "Low Battery Duration."

I thought that the Maximum Required Delay was an alternative to the Low Battery Duration. I.e., the card uses whichever one is greater. Is this not the case?

I'm not configuring anything on the clients yet. I'm just trying to understand the settings on the UPS.

Thanks.
"low battery signal time" simply means estimated runtime remaining before it would signal "low battery".
If you set it for 5, it would signal "low battery" when there's 5 minutes remaining.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Are you saying then that the Shutdown Delay is included in the Low Battery Duration? From my testing, that doesn't seem to be the case.

People on this forum seem to be in the same situation as me, guessing at what these setting actually mean.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

The PCNS clients always shutdown when they receive a low battery signal, I believe. The two minues seems to be an additional time that's documented in the help file, but I'm not sure if the two minutes is always added or not.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:10 AM

0 Likes
0
2548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:10 AM

Unless you specify for the UPS to initiate a shutdown, the PCNS or PCBE clients will not shutdown until their threshold has been violated. In the 10 + 2 + 20 equation, what's the 2 value for?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:25 AM . Last Modified: ‎2024-03-08 12:10 AM

0 Likes
0
2549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:25 AM . Last Modified: ‎2024-03-08 12:10 AM

Hello,

I want to get the maximum battery runtime on the SmartUPS 1400 and I am attempting to understand how the settings in the management card affect when the low battery signal is sent to the clients.

If I set the Low Battery Duration to 2 minutes and the Shutdown Delay to 20 seconds and the Maximum Required Delay is 2 minutes, when does the UPS actually send the low battery signal? With 2 minues left? 4 minues left? 4:20 left?

If I increase the Shutdown delay to 180 seconds, does this cause the low battery signal to be sent 160 seconds sooner? What if I increase the PowerChust command runtime to say 300 seconds so tha the Maximum Required Delay is then 6 minues. Does this cause the low battery signal to then come 4 minutes sooner? This is all very poorly documented.

Any help appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore