Prevent computer from shttung down

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Prevent computer from shttung down
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
3
675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Prevent computer from shttung down

Hello,

- I'm using an old Laptop as a server which it has it's own battery.

- An APC Smart UPS 750VA unit connected to that Laptop via USB.

- Using PowerChute Business Edition 10.0.2.301

- Windows 10 Home x64

 

I have created a simple batch file to safely shutdown my network connected devices to the UPS when a Power Outage occurs.

The problem is while the batch file is running on the Laptop and before it completes, the UPS gives a command to the Laptop to shutdown and it does.

Is there anyway to prevent the Laptop from shutting down? I want the Laptop to stay on for all the time it can on its own battery.
I'm having a little problem understanding how the software works.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:25 AM . Last Modified: ‎2024-03-08 12:10 AM

0 Likes
0
675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:25 AM . Last Modified: ‎2024-03-08 12:10 AM

Hi,

The OS will always be powered off as that is its main purpose. At the bottom of the Shutdown Settings page there is a note explaining this.

Note: Regardless of the Power Outage Configuration selection, if the UPS is On Battery and the remaining UPS runtime falls below the combined time configured for Application and Operating System Shutdown (180 Seconds) then an immediate Shutdown is triggered to ensure enough time for a graceful shutdown.

When PowerChute executes the shutdown sequence an entry is written to the system application log. You can create a command file that would run when PowerChute executes the shutdown sequence. The event you would what to create the task for is APCPBEAgent Event ID: 1025

See this video for assistance with creating the task. https://schneider-electric.box.com/s/6d0hpkq906r9l94sruibfg6c39mwzr2q

The Windows command file would include shutdown /a 

NOTE: Once PowerChute begins the shutdown process the PowerChute web GUI will become unresponsive. If the laptop is not rebooted to access the PowerChute web GUI you will need to restart the APCPBEAgent service. 

 

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Hi,

What version of PowerChute Business Edition are you running and what is the OS?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Sorry about that, edited first post

Also forgot to mention, i have the option " Do not shut down in the event of a power outage. " selected in the "Shutdown Settings" page, But it still does Shutdown like 2 minutes after the Power Outage occurs.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:25 AM . Last Modified: ‎2024-03-08 12:10 AM

0 Likes
0
676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:25 AM . Last Modified: ‎2024-03-08 12:10 AM

Hi,

The OS will always be powered off as that is its main purpose. At the bottom of the Shutdown Settings page there is a note explaining this.

Note: Regardless of the Power Outage Configuration selection, if the UPS is On Battery and the remaining UPS runtime falls below the combined time configured for Application and Operating System Shutdown (180 Seconds) then an immediate Shutdown is triggered to ensure enough time for a graceful shutdown.

When PowerChute executes the shutdown sequence an entry is written to the system application log. You can create a command file that would run when PowerChute executes the shutdown sequence. The event you would what to create the task for is APCPBEAgent Event ID: 1025

See this video for assistance with creating the task. https://schneider-electric.box.com/s/6d0hpkq906r9l94sruibfg6c39mwzr2q

The Windows command file would include shutdown /a 

NOTE: Once PowerChute begins the shutdown process the PowerChute web GUI will become unresponsive. If the laptop is not rebooted to access the PowerChute web GUI you will need to restart the APCPBEAgent service. 

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of