Unable To Start APC PowerChute Service with GMSA Account Logon

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Unable To Start APC PowerChute Service with GMSA Account Logon
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:23 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
12
4598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:23 AM . Last Modified: ‎2024-03-08 12:12 AM

Unable To Start APC PowerChute Service with GMSA Account Logon

My apologies for the duplicate post. I accidentally posted this under the wrong forum category last week,

I am running APC Powerchute for Business on a server running Windows Server 2019. I am attempting to configure graceful unattended shutdown across several servers on our network. In order to do so, I need to provide log on access to the servers in the APC Powerchute service. 

I have created a gMSA account for this purpose. But when I select the account in the log on pane and restart the service I receive the following error.

"Windows could not start the APC PBE Agent service on local computer. Error 1067: The process terminated unexpectedly."

I have deleted the service hkey in regedit and also tried taking the following troubleshooting step.

https://docs.microsoft.com/en-us/troubleshoot/windows-server/performance/service-using-gmsa-account-...

No luck on either. I created a test account and joined it to the domain admin group. This works. For security reasons, I need to use the gMSA account, though. 

 

Any thoughts are greatly appreciated.

 

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Hi Bill,

I was able to make GUS work on a test server when logged in with the local admin account. The issue is that two of the servers I am trying to program GUS on are DCs and DCs do not allow you to login in with local accounts. So it seems like this approach will not work on those servers.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:23 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:23 AM . Last Modified: ‎2024-03-08 12:12 AM

Unable to Logon to Service USing gMSA Account. Hello, I am running APC Powerchute for Business on a server running Windows Server 2019. "Windows could not start the APC PBE Agent service on local computer.

 

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

Windows Service for PowerChute Business Edition Agent does not start. A dialog pop-up message is shown after the service fails to start.

 

Prepaid Card Status

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

Hi,

What is the error that is reported? Is it Windows Event ID 1067 and have you installed PowerChute Agent 10.0.2? Also, where are you located? 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

@bill. Yes. The error is 1067. And yes, I have the most recent version of powerchute installed. Where am I located? Do you mean what Country? State?

 

@Gallimore: I was not able to make the logon to desktop setting work. That is why I tried going the gSMA route. This is not working so as a workaround I have created a test admin account with domain admin rights to log on to the service. This is the only method that is working for me, but it is not the most secure.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
0
4595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

Hi,

What Country? 

To resolve the 1067 error you should uninstall PowerChute Business Edition version 10.0.2 and install version 10.0.1 from this link.

https://schneider-electric.box.com/s/l8rqmw7m5tqgb9v9317w2txotb30uvca

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

HI Bill,

I'm in the US. I will download and test 10.1 tomorrow. Thanks!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Hi,

Before you uninstall PowerChute version 10.0.2 would you please send me a copy of the pcbe.log file that will be found in C:\Program Files (x86)\APC\PowerChute Business Edition\agent\log 

 

Thanks,

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Definitely. Thanks for all the help.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Bill,

I can't figure out how to PM you. Can you private message me or otherwise provide me with an email address to send the log to?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
4596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

@bill : I installed Powerchute 10.1 but am now getting the attached error message (see uploaded screenshot). When I check the System Event Log, this is the summary I find:

"Error: 5, Time out 90 seconds. Service start operation canceled."

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
4595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Kevin,

Have you tried to install using a local admin account? I have seen the 1067 issue when the Admin account is not referenced correctly, so the service fails. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
4597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

Hi Bill,

I was able to make GUS work on a test server when logged in with the local admin account. The issue is that two of the servers I am trying to program GUS on are DCs and DCs do not allow you to login in with local accounts. So it seems like this approach will not work on those servers.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric