SC1000 and HP Proliant Server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SC1000 and HP Proliant Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
4
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

SC1000 and HP Proliant Server

I wanted to confirm that there may be problems with the SC line of UPSs (specifically the SC1000) and HP Proliant ML350 servers. Can anyone confirm that ?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

I wanted to confirm that there may be problems with the SC line of UPSs (specifically the SC1000) and HP Proliant ML350 servers. Can anyone confirm that ?

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

mtanney wrote:
I wanted to confirm that there may be problems with the SC line of UPSs (specifically the SC1000) and HP Proliant ML350 servers. Can anyone confirm that ?
I can't confirm a known incompatibility, but it's been discussed here before and not unheard of in power conditioning industry that an active PFC power supply can sometimes pick a fight with modified square wave UPSs. The Smart-UPS SC may have the same control and monitoring capabilities as the Smart-UPS, but the battery backup inverter is built on the same modified square-wave design used by the consumer grade Back-UPS

After verifying the UPS is actually adequately sized for the UPS and you still experience strange behavior from the server when you pull the plug to the UPS, then there's a conflict.

In this case, your options, you can find a refurbished SU1000NET or SU1400NET on Google search.
If budget allows, you could get a new SUA1500 or SUA1000
These have a sinewave inverter and provides a clean sinewave output even while on battery.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:12 AM

Thanks for the replies. KVAr - what you said sounds like what I've heard before. However I'm a computer tech not an electrician, so it goes a bit over my head. It appears I should stay away from the SC models. For the record, the problem I would run into is the UPS would report an overload, even though 1000VA seemed to be plenty for a Proliant server.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

mtanney wrote:
Thanks for the replies. KVAr - what you said sounds like what I've heard before. However I'm a computer tech not an electrician, so it goes a bit over my head. It appears I should stay away from the SC models. For the record, the problem I would run into is the UPS would report an overload, even though 1000VA seemed to be plenty for a Proliant server.
I really don't know your server. I say get a kill-a-watt power meter online, which is something like $25-30 shipped, then go from there. You can find it easily on Google.

Your SC is rated for 600 Watts / 1000 VA. Check both W & VA. If the two values are pretty darn close to the same, you have active PFC.
Check wattage again and there should be adequate margin between the read value and 600W.

The server shouldn't be pulling much more than 300W. This ensures you have enough power capacity under full load and you don't get too close to the rated maximum, as the runtime drops exponentially as you approach the full rated load on small UPSs.

If you're using a CRT, disable Energy Saver or switch to LCD. If the power is lost while the CRT is in sleep mode and someone wakes it up, the degauss coil that is activated on wake up could cause the UPS to shut off.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

0 Likes
0
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:24 AM . Last Modified: ‎2024-03-08 12:11 AM

I wanted to confirm that there may be problems with the SC line of UPSs (specifically the SC1000) and HP Proliant ML350 servers. Can anyone confirm that ?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login