Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

BE550G battery voltage low

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE550G battery voltage low
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
DaveH52
DaveH52
Cadet

Posted: β€Ž2025-05-24 08:56 PM

0 Likes
6
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-24 08:56 PM

BE550G battery voltage low

My BE550G is not fully charging its battery. The charging voltage is only 12.5V. My other UPSs (BE750G) have battery charging voltage of 12.7V. Is there a simple adjustment inside the unit that I can use to set the voltage?

I found a schematic and I think this is the circuit that controls the charging voltage by adjusting VR1.  I'm a retired EE and have plenty of meters and scopes and stuff, and I'm not afraid to open it up and poke around, but I thought I'd find out if others have run into this problem first.

Attachments
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Next Topic
Replies 6
Teken
Spock Teken
Spock

Posted: β€Ž2025-05-26 02:52 AM

0 Likes
5
105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-26 02:52 AM

How was the battery voltage taken?!?

 

Based on the reading you have provided it would seem it was taken while the battery was disconnected from the system.

 

As the float voltage would be 13.5 ~ 13.8 VDC. While equalize charging the input voltage would be 14.4 ~ 15.XX VDC.

 

Questions Ask . . . πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

DaveH52
DaveH52
Cadet

Posted: β€Ž2025-05-26 08:59 PM

In response to Teken
0 Likes
4
86
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-26 08:59 PM

Teken thanks for replying.

That was the charging voltage with the battery connected and measured with a Fluke 87 DMM. To make matters even worse, I had another battery that had been charged to 13.7V. When I installed it into the BE550G, the serial app said it was 13.7V which is what I expected. What I did not expect was that a day later, it said 13.5V. I have another BE550G, and I tried the same experiment. It started at 13.7V, and a day later it was at 13.5V. I opened one of the BE550Gs to see if there was a voltage adjustment, but I could not find anything to adjust anywhere inside. Apparently, it's set in the UPS firmware, and I have not seen any firmware files anywhere. So, I'm seriously considering trying to sneak a small surface mount regulator board inside both units that I can set to 13.8V so the battery takes more charge. Unfortunately, empty space inside will be a challenge.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: β€Ž2025-05-27 03:28 AM

In response to DaveH52
0 Likes
3
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-27 03:28 AM

A 13.5 VDC float voltage is perfectly fine as this is within the battery makers charging specifications. 

Any voltage that is above 12.80 ~ 12.90 VDC will fully charge and saturate a battery cell. 

Being on the lower floating threshold has the benefit of extending the battery service life as it will not boil out the electrolyte. 

Questions Ask . . . πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

DaveH52
DaveH52
Cadet

Posted: β€Ž2025-05-27 11:29 AM

In response to Teken
0 Likes
2
52
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-27 11:29 AM

That does make some sense, at least about the electrolyte. However, it seems that the BE550G tells me that I've got a considerably longer run-time when the battery has been charged at 3.7V, as opposed to 3.5V. Perhaps I'm just so used to automotive batteries that charge at 13.8V

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: β€Ž2025-05-28 01:45 AM

In response to DaveH52
0 Likes
1
51
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-28 01:45 AM

13.5 ~ 13.8 VDC is the Float voltage not the charging voltage.


The operational runtime seen  / displayed is reflective of the load, battery health, and temperature.

 

A 13.5 VDC Float charge has absolutely no impact whatsoever on the operational runtime.

 

Questions Ask . . . πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

DaveH52
DaveH52
Cadet

Posted: β€Ž2025-05-28 10:12 AM

In response to Teken
0 Likes
0
5
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-05-28 10:12 AM

OK next issue. 

 

One of my BE550Gs does not seem to be showing the % load. 

 

What I've been doing is plugging another computer into a battery-backed outlet, waiting for Micro$oft and all the other start-up SW has settled down and until Task Manager says it's idling at about 1% CPU then telling my browser to reload the page, which also causes the APC software to update. 

 

So this particular BE550G says that it has 475 minutes of runtime and that there is 0% load on it. Now I don't think an intel i7 cpu, spinning HDD, and everything else in that box is capable of running without drawing any power.

 

Do you know how the power consumption or % load is measured inside the BE550? Is there a torroid or other kind of current sense transformer in the BE550 that might have an open winding or a bad solder joint?

 

What I'd really like to get my hands on are schematics for the BE550G and the BE750G UPSs.

 

Again, thanks for putting up with me!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of