BAckUPS CS-350

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
98

BAckUPS CS-350

This question was originally posted by Mel on APC forums on 9/21/2011


I recently aquired a BackUPS CS-350 that has an issue. The unit powers on soon as it is plugged in to the receptacle without the power being pressed and it will not power off from the power switch . However if the power switch is pressed while the unit is on it performs the battery test. How can the power switch be made to work normally is this a programmable function?


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
98

Re: Back-UPS CS-350

This reply was originally posted by Jonathan on APC forums on 9/21/2011


Good day Mel,

The UPS that you have does not behave the way that it should. You should be able to use the button to turn on/off the unit. Where did you got this unit from and do you have the exact model number of the UPS?

Let us see if the steps outlined below would help:
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket.
3: Disconnect the UPS' internal battery.
4: Push and hold the "On" button on the UPS for 5 seconds.
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.

In the event that the UPS continues to turn on as soon as you plug it in to an input power source, I suggest that you contact the APC support team for your region to verify the warranty status of the UPS. If it is within warranty, it merits a replacement.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
99

Re: Back-UPS CS-350

This reply was originally posted by Jonathan on APC forums on 9/21/2011


Good day Mel,

The UPS that you have does not behave the way that it should. You should be able to use the button to turn on/off the unit. Where did you got this unit from and do you have the exact model number of the UPS?

Let us see if the steps outlined below would help:
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket.
3: Disconnect the UPS' internal battery.
4: Push and hold the "On" button on the UPS for 5 seconds.
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.

In the event that the UPS continues to turn on as soon as you plug it in to an input power source, I suggest that you contact the APC support team for your region to verify the warranty status of the UPS. If it is within warranty, it merits a replacement.