Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

APC Back-UPS ES 550 not shutting down computer during an outage/surge

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: APC Back-UPS ES 550 not shutting down computer during an outage/surge
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
148
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:09 PM . Last Modified: ‎2024-03-20 05:45 AM

0 Likes
5
2354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:09 PM . Last Modified: ‎2024-03-20 05:45 AM

APC Back-UPS ES 550 not shutting down computer during an outage/surge

Hello.

I have a APC Back-UPS ES 550 running on a 64 bit Windows 7 system with Powerchute Personal Edition 3.0.2. Powerchute is not shutting down the computer at all during an outage/surge. The computer simply loses power without shutting down safely and dies due to the lack of power.

The options are set to "keep my computer on as long as possible" at 5 minutes. Sensitivity is set to high. Voltage sensitivity is set to above 139 and a below 88. The current voltage usually stays at around 119 during regular usage.

The Windows power options are set to never turn off display, never put the computer to sleep, never turn off hard disks, never sleep, never hybrid sleep, never hibernate.

The APC Back-UPS ES 550 has a solid green light always on and does not beep during regular usage. The router, monitor, and PC are connected to battery backup/surge protection. The printer and speakers are connected to surge protection only. Powerchute says "your battery backup is operating normally". The current status is electrical power is being supplied by AC utility power, remaining battery charge is 100%, estimated battery time 46 minutes, power source AC utility power. The APC Back-UPS ES 550 and its battery are several years old. I'm using an identical unit with another computer in the same room and it does not have any problems.

Please help. Thank you.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:45 AM

0 Likes
0
2354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:45 AM

Ok, this could just be that the battery cannot support the load. And yes, by PowerChute detecting the UPS, I am referring to see the UPS information in the software as you noted.

I would start by removing the computer and plugging something simple in like a lamp or similar to the battery back up outlets and then simulate a power failure by unplugging the UPS from the wall and see if the UPS supports the lamp compared to how it does not support your computer. Make sure to turn off and you unplug your computer as well as the USB cable temporarily.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:09 PM . Last Modified: ‎2024-03-20 05:45 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:09 PM . Last Modified: ‎2024-03-20 05:45 AM

  • Did this ever work properly with this set up?
  • Does the UPS switch to battery power during the outage and beep 4 times every 30 seconds?
  • After how long does the computer turn off?
  • Is there anything interesting in Administrative Tools->Event Viewer on your computer?
  • In PowerChute, have you left the program running and see when the UPS goes to battery that it reports that status change correctly?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:09 PM . Last Modified: ‎2024-03-20 05:45 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:09 PM . Last Modified: ‎2024-03-20 05:45 AM

- Yes, this has worked properly with this setup in the past, since I never had a problem with the UPS not intervening like now. Does anything need to be set up differently for Windows 7?

- When there was a surge, the computer just lost complete power on the spot, dead. The UPS did not intervene in any way. When there was an outage, the same exact thing happened.

- The computer loses power instantly during a surge or outage. Going dead on the spot.

- There are 2 critical events showing for the past 7 days. What exactly am I looking for there?

- It does report the changes accurately. The only thing that doesn't make sense is that it says "time on battery: 3 hours 44 minutes", which is not true at all, since the computer just dies on the spot, without UPS intervention when a surge or outage happens.

Thank you for helping.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:09 PM . Last Modified: ‎2024-03-20 05:45 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:09 PM . Last Modified: ‎2024-03-20 05:45 AM

Thanks for the feedback. Here is some more from me:

  • Nope, nothing different for Windows 7 if you've gotten PowerChute going and it detects the UPS.
  • Does the UPS turn off itself during power events or does it remain on after all your equipment has powered down?
  • In Administrative Tools->Event Viewer, I was just looking for any events related to the UPS. I wasn't sure what would be there but just anything relating to power loss.
  • How old is the UPS and what is the exact model? This is located on the back or bottom. I would also like the first six characters of the serial number (i.e. JB0947) to help tell the age and let me know if you've ever replaced the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:45 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:45 AM

- By Powerchute detecting the UPS, do you mean it saying "your battery backup is operating normally"?

- The UPS remained on even though the PC was dead as soon as the surge happened. I was asleep during the blackout but I know the PC was not powered down properly. It was killed off due to the lack of power support.

- I didn't notice anything about power loss, but to be honest, I'm not really sure what I'm looking for in the Event Viewer. smile

- The UPS is at least 5 years old. I have never changed the battery.

Thanks again for helping. I really hope to fix this as soon as possible.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:45 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:10 PM . Last Modified: ‎2024-03-20 05:45 AM

Ok, this could just be that the battery cannot support the load. And yes, by PowerChute detecting the UPS, I am referring to see the UPS information in the software as you noted.

I would start by removing the computer and plugging something simple in like a lamp or similar to the battery back up outlets and then simulate a power failure by unplugging the UPS from the wall and see if the UPS supports the lamp compared to how it does not support your computer. Make sure to turn off and you unplug your computer as well as the USB cable temporarily.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore