Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

what is the input voltage tolerance acceptable range of UPS Model: SUVT

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • what is the input voltage tolerance acceptable range of UPS Model: SUVT
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:50 PM

0 Likes
4
3428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:50 PM

what is the input voltage tolerance acceptable range of UPS Model: SUVT

Hello ,

I am getting frequent alerts as below mentioned .

Name     : APC SUVT 15KVA

Code: 0x0210

Informational - UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

after download Data log & filtering we found 

UPS - B

 

Date

20-Aug-18

Time

9:06:17

Vmin1

220.6

Vmin2

205.7

Vmin3

226.3

%

91%

20-Aug-18

8:56:17

221.4

205.9

222.9

92%

20-Aug-18

8:46:17

222.5

208.3

221.9

94%

20-Aug-18

8:36:17

221.1

209

221.3

94%

20-Aug-18

8:26:17

221.2

205.3

222

92%

20-Aug-18

8:16:17

220.2

207.4

223.1

93%

20-Aug-18

8:06:17

221.4

205.5

224.5

92%

20-Aug-18

7:56:17

222.9

209.7

226.8

92%

20-Aug-18

7:46:17

225

212.4

226.6

94%

 

UPS – A

 

8/20/18

9:08:49

222.2

205

225.4

91%

8/20/18

8:58:49

220.7

206.3

222

93%

8/20/18

8:48:49

223.2

207.6

222.9

93%

8/20/18

8:38:49

221.1

208.3

222.1

94%

8/20/18

8:28:49

221.6

204.5

221

92%

8/20/18

8:18:49

222.2

207

224.7

92%

8/20/18

8:08:49

221.3

205.1

223.8

92%

8/20/18

7:58:49

223.5

209

223.8

93%

8/20/18

7:48:49

224.9

212

227.8

93%

by compare between phase1, phase2, phase3 the difference voltage is 6% - 9%. 

what is the acceptable rage of UPS input voltage ? Less than 5%?

Please advice.

Thanks,

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

0 Likes
0
3427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

Dear All,

As attached file I have capture from my ups Model SUVT. The event log shown the calibration is start & completed, But I don't know who was do it or it was automatic start by UPS its self or it does by virus or else? please kindly advise.

Thanks,

Veasna.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:50 PM

0 Likes
0
3427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:50 PM

Hi Veasna

This event also occurs not only for voltage fluctuations but also when there is interference and noise on the input waveform, which is most likely the cause here.

The logs are only giving you a 5 minute interval snapshot of the voltages as well, putting a power analyser on the utility power will give you a much more complete picture of what is going on.

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:50 PM

0 Likes
0
3427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:50 PM

Hi Matt,

Thanks for your answer.

I would like to attached file Data log & Event log

could you help analyze what is the root cause & issue?

Thanks,

Veasna.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:50 PM

0 Likes
0
3427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:50 PM

Hi Veasna

At this point it would be best to call your local APC technical support on +855-23-964-311 or using this Contact Form , so it can be handled by agents who deal with the SUVT product.

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

0 Likes
0
3428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

Dear All,

As attached file I have capture from my ups Model SUVT. The event log shown the calibration is start & completed, But I don't know who was do it or it was automatic start by UPS its self or it does by virus or else? please kindly advise.

Thanks,

Veasna.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore