Hello ,
I am getting frequent alerts as below mentioned .
Name : APC SUVT 15KVA
Code: 0x0210
Informational - UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
after download Data log & filtering we found
UPS - B
Date 20-Aug-18 |
Time 9:06:17 |
Vmin1 220.6 |
Vmin2 205.7 |
Vmin3 226.3 |
% 91% |
20-Aug-18 |
8:56:17 |
221.4 |
205.9 |
222.9 |
92% |
20-Aug-18 |
8:46:17 |
222.5 |
208.3 |
221.9 |
94% |
20-Aug-18 |
8:36:17 |
221.1 |
209 |
221.3 |
94% |
20-Aug-18 |
8:26:17 |
221.2 |
205.3 |
222 |
92% |
20-Aug-18 |
8:16:17 |
220.2 |
207.4 |
223.1 |
93% |
20-Aug-18 |
8:06:17 |
221.4 |
205.5 |
224.5 |
92% |
20-Aug-18 |
7:56:17 |
222.9 |
209.7 |
226.8 |
92% |
20-Aug-18 |
7:46:17 |
225 |
212.4 |
226.6 |
94% |
UPS – A
8/20/18 |
9:08:49 |
222.2 |
205 |
225.4 |
91% |
8/20/18 |
8:58:49 |
220.7 |
206.3 |
222 |
93% |
8/20/18 |
8:48:49 |
223.2 |
207.6 |
222.9 |
93% |
8/20/18 |
8:38:49 |
221.1 |
208.3 |
222.1 |
94% |
8/20/18 |
8:28:49 |
221.6 |
204.5 |
221 |
92% |
8/20/18 |
8:18:49 |
222.2 |
207 |
224.7 |
92% |
8/20/18 |
8:08:49 |
221.3 |
205.1 |
223.8 |
92% |
8/20/18 |
7:58:49 |
223.5 |
209 |
223.8 |
93% |
8/20/18 |
7:48:49 |
224.9 |
212 |
227.8 |
93%
|
by compare between phase1, phase2, phase3 the difference voltage is 6% - 9%.
what is the acceptable rage of UPS input voltage ? Less than 5%?
Please advice.
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:45 AM . Last Modified: 2024-03-17 11:49 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:45 AM . Last Modified: 2024-03-17 11:49 PM
Dear All,
As attached file I have capture from my ups Model SUVT. The event log shown the calibration is start & completed, But I don't know who was do it or it was automatic start by UPS its self or it does by virus or else? please kindly advise.
Thanks,
Veasna.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:45 AM . Last Modified: 2024-03-17 11:50 PM
Hi Veasna
This event also occurs not only for voltage fluctuations but also when there is interference and noise on the input waveform, which is most likely the cause here.
The logs are only giving you a 5 minute interval snapshot of the voltages as well, putting a power analyser on the utility power will give you a much more complete picture of what is going on.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:45 AM . Last Modified: 2024-03-17 11:50 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:45 AM . Last Modified: 2024-03-17 11:50 PM
Hi Veasna
At this point it would be best to call your local APC technical support on +855-23-964-311 or using this Contact Form , so it can be handled by agents who deal with the SUVT product.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:45 AM . Last Modified: 2024-03-17 11:49 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:45 AM . Last Modified: 2024-03-17 11:49 PM
Dear All,
As attached file I have capture from my ups Model SUVT. The event log shown the calibration is start & completed, But I don't know who was do it or it was automatic start by UPS its self or it does by virus or else? please kindly advise.