Another blown fuse in SU3000

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Another blown fuse in SU3000
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

0 Likes
5
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

Another blown fuse in SU3000

Have one of some SU3000 at different sites up and running since early 2017. During a power outage on one site the ups turned off as configured and expected. After power has been restored the UPS didn't come back due to a blown fuse in the distribution box. Bringing the fuse back by hand, the UPS turns on again with all the attached devices. This issue can be reproduced using the same fuse or another one in the distribution box. The fuse we're using here in Germany is standard model with 16 amps.

What may the cause? The UPS power supply? The power cord (can't believe)? Other?

Thanks, David

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:46 AM . Last Modified: ‎2024-03-17 11:49 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:46 AM . Last Modified: ‎2024-03-17 11:49 PM

Hi Szabi,

thank you very much for your response and the explanation! I really would like to find this in the manual! Will contact APC Germany for a statement.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

Hi David - 

Can I get the exact model and serial number of your Smart-UPS? Are you using Network management Cards or Powerchute Business Edition? If so, have they logged any faults?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

Hi Liam,

Model is SMT3000RMI2U, SN AS1616164956. We're using NMC2 with PCNS (no Business Edition). And no, there are no suspicious log entries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:45 AM . Last Modified: ‎2024-03-17 11:49 PM

Any news regarding this issue. We don't want to wait for the next unexpected power outage...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:46 AM . Last Modified: ‎2024-03-17 11:49 PM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:46 AM . Last Modified: ‎2024-03-17 11:49 PM

Hi David,

Under the usual 230V input conditions, a 16A breaker would already be a borderline choice for the SMT3000RMI2U, due to the UPS internal power consumption and charger. On top of this, the lowest acceptable input voltage for online operation for the SMT3000RMI2U is 160V. As input voltage decreases, current draw increases in order to deliver the same power to the load, so for example, at full load, this UPS could end up drawing 3000VA/160V=18.75A + additional internal power consumption. A 20A upstream breaker, or fuse, is recommended, even if the circuit is dedicated to feeding the UPS only.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:46 AM . Last Modified: ‎2024-03-17 11:49 PM

0 Likes
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:46 AM . Last Modified: ‎2024-03-17 11:49 PM

Hi Szabi,

thank you very much for your response and the explanation! I really would like to find this in the manual! Will contact APC Germany for a statement.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now