upsAdvStateAbnormalConditions returns empty string

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • upsAdvStateAbnormalConditions returns empty string
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:31 AM

0 Likes
3
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:31 AM

upsAdvStateAbnormalConditions returns empty string

If we query the AP9630 or AP9617 management module on Smart-UPS RT 3000 XL with SNMP for upsAdvStateAbnormalConditions, we get an empty string.

We have upgraded to firmware 5.1.5.

Issues are with the SURTD3000XLI with the AP9617 and AP9630.

Model: Smart-UPS RT 3000 XL
Serial Number: NS0918002036
Firmware Revision: 4.1 (ID5)
Manufacture Date: 04/30/2009

snmpget -On -v1 -c public UPS .1.3.6.1.2.1.1.1.0
snmpget -On -v1 -c public UPS .1.3.6.1.4.1.318.1.1.1.11.2.1.0

.1.3.6.1.2.1.1.1.0 = STRING: APC Web/SNMP Management Card (MB:v4.0.1 PF:v5.1.5 PN:apc_hw05_aos_515.bin AF1:v5.1.5 AN1:apc_hw05_sumx_515.bin MN:AP9630 HR:05 SN: BA0915014135 MD:04/11/2009) (Embedded PowerNet SNMP Agent SW v2.2 compatible)
.1.3.6.1.4.1.318.1.1.1.11.2.1.0 = ""

Expected is
.1.3.6.1.4.1.318.1.1.1.11.2.1.0 = STRING: "00000000000000000000000000000000"

Is anybody else experiencing the same problem?

Thanks in advance.

Mark

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • .1.3.6.1.4.1.318.1.1.1.11.2.1.0
  • ap9617
  • ap9630
  • empty_string
  • network_management_card
  • snmp
  • surtd3000xli
  • upsadvstateabnormalconditions
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:45 AM . Last Modified: ‎2024-03-11 12:31 AM

0 Likes
0
746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:45 AM . Last Modified: ‎2024-03-11 12:31 AM

hi mark,

i mis-read your initial post and saw the reply of all zeros and thought thats what you got back which was a line below when you said got "" - sorry about that!

actually, i found that we have an issue logged against this for the SURTD3000XLI model. it will be fixed in sumx 6.x which i think will be available later this year but essentially it is an NMC firmware bug with that particular UPS. it won't get addressed on AP9617 based management cards because those are discontinued now.

hope that helps!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:31 AM

0 Likes
0
746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:44 AM . Last Modified: ‎2024-03-11 12:31 AM

this string should only have data when there is an abnormal condition present. to me, this looks normal if your UPS is running just fine.

here is the description of the OID which i found by using a MIB browser (keep in mind not every UPS supports every condition listed below:

An ASCII string containing the 32 flags representing the current active UPS faults. If the Network Card is unable to determine the values of the flags, this
variable is set to 'UNKNOWN'. If this variable is not supported by the connected UPS, this variable is set to 'NOT SUPPORTED'.

The flags are numbered from 1 to 32, and read from left to right. The flags are defined as follows:

Flag 1: Power Module Failure
Flag 2: Main Intelligence Module Failure
Flag 3: Redundant Intelligence Module Failure
Flag 4: Battery Failure

Flag 5: Load(kVA) Alarm Threshold Violation
Flag 6: Redundancy Lost
Flag 7: Redundancy Below Alarm Threshold
Flag 8: Bypass not in Range; Either Frequency or Voltage

Flag 9: Bypass Contactor Stuck in Bypass Condition
Flag 10: Bypass Contactor Stuck in On-Line Condition
Flag 11: In Bypass due to an Internal Fault
Flag 12: In Bypass due to an Overload

Flag 13: In Maintenance Bypass
Flag 14: Input Circuit Braker Tripped Open
Flag 15: System Level Fan Failure
Flag 16: Redundant Intelligent Module in Control

Flag 17: IIC Inter-Module Communication Failure
Flag 18: No Working Power Modules
Flag 19: Load Shutdown From Bypass; Input Frequency
Flag 20: Runtime Below Alarm Threshold

Flag 21: Extended Run Frame Fault
Flag 22: Output Voltage out of Range
Flag 23: UPS Not Synchronized
Flag 24: No Batteries Installed

Flag 25: Battery Voltage High
Flag 26: UPS Specific Fault Detected
Flag 27: Site Wiring Fault
Flag 28: Backfeed Protection Relay Opened

Flag 29:
Flag 30:
Flag 31:
Flag 32:

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:45 AM . Last Modified: ‎2024-03-11 12:31 AM

0 Likes
0
746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:45 AM . Last Modified: ‎2024-03-11 12:31 AM

Thanks for your reply.

In the forum, part of your message is truncated. However, the full text is in the email notification.

From the MIB file:

An ASCII string containing the 32 flags representing the current active UPS faults.
If the Network Card is unable to determine the values of the flags, this
variable is set to 'UNKNOWN'. If this variable is not supported by the
connected UPS, this variable is set to 'NOT SUPPORTED'.

My interpretation is that there are three possibilities:

.1.3.6.1.4.1.318.1.1.1.11.2.1.0 = STRING: "00000000000000000000000000000000"
(a zero may be one if a condition is met)
.1.3.6.1.4.1.318.1.1.1.11.2.1.0 = STRING: "UNKNOWN"
.1.3.6.1.4.1.318.1.1.1.11.2.1.0 = STRING: "NOT SUPPORTED"

An empty string is not a valid option, it is not specified in the MIB file.

We also have a 3000 RM XL UPS, that does return
.1.3.6.1.4.1.318.1.1.1.11.2.1.0 = STRING: "00000000000000000000000000000000"
as expected.

Is there a way to force a flag to be 1 on a SURTD3000XLI, so we can check if the string is correctly returned if one of the flags is set to 'one'?

Regards, Mark

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:45 AM . Last Modified: ‎2024-03-11 12:31 AM

0 Likes
0
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:45 AM . Last Modified: ‎2024-03-11 12:31 AM

hi mark,

i mis-read your initial post and saw the reply of all zeros and thought thats what you got back which was a line below when you said got "" - sorry about that!

actually, i found that we have an issue logged against this for the SURTD3000XLI model. it will be fixed in sumx 6.x which i think will be available later this year but essentially it is an NMC firmware bug with that particular UPS. it won't get addressed on AP9617 based management cards because those are discontinued now.

hope that helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of