Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

upgrade failed

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: upgrade failed
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
skippy_apc
Crewman skippy_apc
Crewman

Posted: ‎2021-07-01 04:20 AM

0 Likes
6
522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:20 AM

upgrade failed

This was originally posted on APC forums on 9/9/2013


I have a UPS with an old AP9617 card. It was old enough that it needed the two step upgrade. Using the wizard I just downloaded to a windows laptop, it did the first upgrade phase and then choked on the second round.

Here's the log file, redacted for my IP address:

Checking network connection ...  Checking version information ...

*************** Next **************

Before Upgrading the NMC the AOS is: apc_hw02_aos_102.bin

* Detected early version, two AOS upgrades required

Attempting to log in to 128.xxx.xxx.xxx ... Log in sucessful

Loading OS, please wait ...                      OK

Please wait (2 minutes ) for system restart   OK

Attempting connection to verify restart        OK

Attempting to log in to 128.xxx.xxx.xxx ... Log in sucessful

Loading OS, please wait ...                      OK

Please wait (2 minutes ) for system restart   OK

Attempting connection to verify restart  Failed to ping at 128.xxx.xxx.xxxSystem reboot failed. Aborting this Upgrade.

Not all Network Management Cards were upgraded successfully:

  128.xxx.xxx.xxx: The Management Card at this address is not responsive.

Encountered 1 failures during upgrade.

================

Now I can ping the device, and when I connect with a browser it tells me

Error: The application was not able to load.
You are attempting to access an APC device.

There was a problem loading the application. Please login to the device via telnet for more details.

That appears in the browser window.  Both telnet and ssh are refusing my connection attempt.

I am probably going to start a hunt for one of those magic RS-232 cables to go plug into the thing. I am looking for advice on what might be the right next step.

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9617
  • failure
  • upgrade
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:20 AM

0 Likes
0
521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:20 AM

This reply was originally posted by Angela on APC forums on 9/10/2013


Ok, go ahead and connect to your card and put sumx372.bin file (which the exact file name is a little different) on there (assuming its a Smart UPS you're trying to put the AP9617 in).

Looks like you have the AOS loaded already so that is why we will go with the application file.

So, connect in and do:

> bin (for binary transfer mode which is required)

> hash

> put or drag and drop it from your desktop if on Windows after you type put and it will paste the file name for you.

Then press enter, then type bye to disconnect. Hopefully with what I said, maybe the instructions are a little easier to understand. You'll only need to update the application instead of the AOS for what I am asking.

See Answer In Context

Reply
Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:20 AM

0 Likes
0
522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:20 AM

This reply was originally posted by Angela on APC forums on 9/10/2013


I would FTP to the card and see if that works. If it does, do the ls command and tell me what files you see there in the file listing. Also, if the FTP prompt pops up, let me know what it says for the AOS version. For example:

C:\Users\>ftp 192.168.1.45

Connected to 192.168.1.45.

220 AP9617 Network Management Card AOS v3.7.3 FTP server ready.

User (192.168.1.45):(none)):

We can probably just try a manual FTP upgrade as the next step with the bin files and the order will depend on what files are currently on the card. Instructions are here -> How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US

Reply
skippy_apc
Crewman skippy_apc
Crewman

Posted: ‎2021-07-01 04:20 AM

0 Likes
0
523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:20 AM

This was originally posted on APC forums on 9/10/2013


Yes, FTP is working. Directory listing:

ftp> ls

227 Entering Passive Mode (128,114,130,214,200,117).

125 Data connection already open; transfer starting.

--wx-wx-wx  1 apc      apc      1572864 Feb 02  2010 apc_hw02_aos_373.bin

drwxrwxrwx  1 apc      apc            0 Feb 02  2010 sec/

226 Closing data connection.

=========

I find the instructions confusing. But FTP access seems hopeful. Let ne know what to do next.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:20 AM

0 Likes
0
522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:20 AM

This reply was originally posted by Angela on APC forums on 9/10/2013


Ok, go ahead and connect to your card and put sumx372.bin file (which the exact file name is a little different) on there (assuming its a Smart UPS you're trying to put the AP9617 in).

Looks like you have the AOS loaded already so that is why we will go with the application file.

So, connect in and do:

> bin (for binary transfer mode which is required)

> hash

> put or drag and drop it from your desktop if on Windows after you type put and it will paste the file name for you.

Then press enter, then type bye to disconnect. Hopefully with what I said, maybe the instructions are a little easier to understand. You'll only need to update the application instead of the AOS for what I am asking.

Reply
skippy_apc
Crewman skippy_apc
Crewman

Posted: ‎2021-07-01 04:20 AM

0 Likes
0
522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:20 AM

This was originally posted on APC forums on 9/10/2013


Thank you.  Only about 99 more to upgrade. . . smile

Reply
skippy_apc
Crewman skippy_apc
Crewman

Posted: ‎2021-07-01 04:21 AM

0 Likes
0
522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:21 AM

This was originally posted on APC forums on 9/13/2013


I have now upgraded six 9617s with the windows PC program. In all cases, the PC program fails and leaves the management module with the new OS program running but the application (sumx) not loaded.  In all cases, the manual FTP rescue works.

What I found is that the windows application says it will wait 2 minutes for the mgmt module to reboot.  It then commences looking for it on the net. It tries to contact it for about 30 seconds and then the program gives up.  The time required for this reboot to complete and the mgmt module to resume answering pings is about 3.5 minutes.  So by the time the first reboot is finished, the Windows upgrade application has packed it in and gone home. I am running the application on XP Service Pack 2. It is not that the mgmt card does not reboot, it is that it doesn't do it as fast as the application thinks it should.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:21 AM

0 Likes
0
523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 04:21 AM

This reply was originally posted by Angela on APC forums on 9/13/2013


Yes, I've seen that before but not every time. The timing seems to be off a little bit. It probably depends on the version and size of the files loaded and which application which contributes to the timing. Glad it is all set though.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc