unexpected shutdown with SRT1500RMXLI ups

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • unexpected shutdown with SRT1500RMXLI ups
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
pazzoide76
Crewman pazzoide76
Crewman

Posted: ‎2022-01-12 12:24 AM

0 Likes
3
1179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-12 12:24 AM

unexpected shutdown with SRT1500RMXLI ups

Hi,
I have a Smart-UPS SRT 1500 with SRT48RMBP battery pack.
During the days of 12/30 and 12/31 the ups switched off the outlet groups after 7 seconds that the battery had entered due to Bypass not in range; low voltage and for Bypass not in range; either frequency or voltage.
This is the log:
12/30/2021 20:06:39 Device UPS: The output power is now turned on.
12/30/2021 20:06:31 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
12/30/2021 20:06:31 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
12/30/2021 20:06:30 Device UPS: RFC1628 MIB alarm entry added.
12/30/2021 20:06:30 Device UPS: The output power is turned off.
12/30/2021 20:06:30 Device UPS: The graceful shutdown period has ended.
12/30/2021 20:05:28 Device UPS: A site wiring fault exists.
12/30/2021 20:05:19 Device UPS: RFC1628 MIB alarm entry removed.
12/30/2021 20:05:19 Device UPS: RFC1628 MIB UPS is no longer battery.
12/30/2021 20:05:19 Device UPS: No longer on battery power.
12/30/2021 20:05:18 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
12/30/2021 20:05:01 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown, sequenced.
12/30/2021 20:05:01 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown, sequenced.
12/30/2021 20:04:55 Device UPS: RFC1628 MIB UPS is on battery.
12/30/2021 20:04:55 Device UPS: On battery power in response to rapid change of input.
12/30/2021 20:04:55 Device UPS: Bypass not in range ; low voltage.

 


12/31/2021 00:14:38 Device UPS: The output power is now turned on.
12/31/2021 00:14:30 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
12/31/2021 00:14:30 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
12/31/2021 00:14:29 Device UPS: RFC1628 MIB alarm entry added.
12/31/2021 00:14:29 Device UPS: The output power is turned off.
12/31/2021 00:14:29 Device UPS: The graceful shutdown period has ended.
12/31/2021 00:13:28 Device UPS: A site wiring fault exists.
12/31/2021 00:13:18 Device UPS: RFC1628 MIB alarm entry removed.
12/31/2021 00:13:18 Device UPS: RFC1628 MIB UPS is no longer battery.
12/31/2021 00:13:18 Device UPS: No longer on battery power.
12/31/2021 00:13:18 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
12/31/2021 00:13:00 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown, sequenced.
12/31/2021 00:13:00 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown, sequenced.
12/31/2021 00:12:53 Device UPS: RFC1628 MIB UPS is on battery.
12/31/2021 00:12:53 Device UPS: On battery power in response to rapid change of input.
12/31/2021 00:12:53 Device UPS: Bypass not in range ; either frequency or voltage.

 

Why did this happen?
Shouldn't there be more time before shutting down the outlet groups?

 

Thank you

 

Greetings

Labels
  • Labels:
  • Other Environmental Monitoring Products & Questions
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-01-13 12:53 AM

0 Likes
2
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-13 12:53 AM

Hi

 

Well, 7 seconds isn't really that useful..

 

That being said, I wonder if you have tried a runtime calibration on the unit, just to check if the batteries are performing?
If they come out OK, I would suggetst downloading the support file from the card and contact your local CCC, to have them look at the information in the file.

 

You can get the support file by logging on to the card and navigating to [About] -> [Support] and choose "Generate Logs".
The Card should then proceed with generating a .tar file with the text files from the NMC and once done you should be able to download it.

 

Contact info for your local CCC team can be found on APC.com -> https://www.apc.com/us/en/support/contact-us/
Just remeber to change coutry on the top of the page to get the correct info.

 

BR
/Tonny

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

pazzoide76
Crewman pazzoide76
Crewman

Posted: ‎2022-01-13 07:12 AM

In response to TonKei
1 Like
1
1156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-13 07:12 AM

Thanks Tonny for your reply.
The UPS model is SRT1500RMXLI and has UPS firmware version 07.3 (ID1025).
Is there an updated firmware to try to install?
Can runtime calibration be done hot with the servers turned on? Can it cause disruptions?

 

Thank you

 

Greetings

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-01-13 08:08 AM . Last Modified: ‎2022-01-13 10:34 PM

In response to pazzoide76
0 Likes
0
1152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-13 08:08 AM . Last Modified: ‎2022-01-13 10:34 PM

Hi

 

Under normal circumstances The unit is designed to be able to do the runtime calibration without causing a disruption to your operation under normal circumstances. But, defect batteries can in certain instances cause the unit to drop the load, and as it is the battery health we want to investigate in this case I would suggest doing the calibration in a service window, just to be on the safe side.

You can find more information on the runtime calibration here -> https://www.apc.com/us/en/faqs/FA284198/

 

Upgrading firmware on the UPS is generally not suggested, unless there is a specific issue that we know can be fixed with the upgrade.

So, getting a ticket opened in the Customer Care Center and getting the support file to them is probably the best way to go right now. Just to get the right people look at the data from your unit.

 

That being said, this kind of issue is rarely related to the UPS firmware in my experience.

 

BR

/Tonny

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of