tower Smart UPS 1400 doesn't power on

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • tower Smart UPS 1400 doesn't power on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
10
3050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

tower Smart UPS 1400 doesn't power on

I'd love to put this old UPS back into service. It was in a closet, sitting unused when I started the job. Today I plugged it in to try to check whether the batteries were good. The UPS doesn't power on, no lights, no beeps. The outlet is definitely providing clean power, and I've tried pushing in the circuit breaker reset on the UPS.

I checked the manual, and the troubleshooting steps don't suggest anything else. Is this the symptom you get if the batteries are very, very dead? The batteries are plugged in at the gray connector, but maybe they're providing zero charge so the UPS doesn't power-on?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

Same symptoms as original post. No power, no beeps, to lights, nothing. Battery voltage is good (26VDC). Good Continuity from outlet to circuit board. Good continuity from battery packs to circuit board. That's where is all ends, at the board.

Replace the board? If so, anyone recommend a place to find replacement/repair parts for this model? (APC 1400 RM)
-or-
Trash it?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

If you can, try metering the voltage on that gray connector. This will rule out if the batteries are dead or if the UPS is toast. Judging by the UPS just sitting around, its a good guess that the batteries are most likely toast. They have about a 6 month shelf life if they arent being charged.

Voltage on the gray connector should be around 25-27 VdC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

Should I read that as:
if the UPS doesn't read 25-27 VDC from the battery pack, as measured at the gray connector, the power-on will silently fail, and not give a bad battery indicator?

I think the batteries are probably bad. I just wanted to know if this is the expected UPS behavior if the batteries are totally bad. Maybe the bank of leds indicating battery life only work if the UPS gets a sufficiently high output from the battery pack?

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

If the batteries are completely dead, the UPS will give no sign of life. Our new units have the capability to power on without the batteries connected, but the 1400 units will not be able to without a good battery.

Message was edited by: EZ Button

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

Thank you very much.

That's exactly what I wanted to know. I was somewhat worried that something else was wrong with the UPS. Time to order a new battery pack!

I can actually understand why this would be the design decision. If the UPS was new and the customer hadn't hooked up the battery pack, it would probably be a good idea for the UPS to not power on until they attached the pack. I also think it is better that the UPS say something that indicates the equivalent of "no battery detected". It's good to hear that's the way the newer models work.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

I'd love to put this old UPS back into service. It was in a closet, sitting unused when I started the job. Today I plugged it in to try to check whether the batteries were good. The UPS doesn't power on, no lights, no beeps. The outlet is definitely providing clean power, and I've tried pushing in the circuit breaker reset on the UPS.

I checked the manual, and the troubleshooting steps don't suggest anything else. Is this the symptom you get if the batteries are very, very dead? The batteries are plugged in at the gray connector, but maybe they're providing zero charge so the UPS doesn't power-on?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

Same symptoms as original post. No power, no beeps, to lights, nothing. Battery voltage is good (26VDC). Good Continuity from outlet to circuit board. Good continuity from battery packs to circuit board. That's where is all ends, at the board.

Replace the board? If so, anyone recommend a place to find replacement/repair parts for this model? (APC 1400 RM)
-or-
Trash it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

APC supports two options:

1.you can trade your ups in through the APC trade-ups program for up to 35% off a new ups. APC will also cover the return shipping cost of the old ups.

2. You can contact Coastal Business Machines to see if they can refurbish the ups. There web page is http://cbmi.com

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

aria wrote:
Same symptoms as original post. No power, no beeps, to lights, nothing. Battery voltage is good (26VDC). Good Continuity from outlet to circuit board. Good continuity from battery packs to circuit board. That's where is all ends, at the board.

Replace the board? If so, anyone recommend a place to find replacement/repair parts for this model? (APC 1400 RM)
-or-
Trash it?
I'm not totally sure, but the SU1400RM2U's RBC24 might be a 48v nominal. If you have the same unit in working conditions, check the battery voltage through PowerChute. If it's around 52v, you have a 48v system, in which case 26v may not be enough to bring the unit out of lockout mode.

Message was edited by: KVAr

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

No, it's made of 4.
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=RBC24

APC gives 432 nominal-V x Ah. If you divide it 48v, you get 9Ah, so the OEM is made of 12v 9Ah packs. Most likely 4 in series. Could be two strings of two in parallel, but I doubt it. If you know what you're doing, it's easy to take it apart and figure it out.

12v 7,7.2,8 and 9Ah all have the same foot print. 9Ah is not as common in the aftermarket replacement market as the 7.2Ah, which can be assembled into RBC24 and if you assemble a replacement battery pack using 7.2Ah, you won't get the same runtime the UPS was designed to provide.

Without knowing the wiring of each battery pack, you have no idea what the voltage is.

Here is what I know for sure:
RBC7 =half U battery x 2 back to back, 17-18Ah, two x 12v series. 24v
RBC6 =12v 12Ah x 2 in series 24v

yes, it is possible for rack and tower versions to have different voltages. For the units using RBC7 (tower type 1400 and 1500 models), if your battery is much below 20v or so, the UPS may not turn on and if the voltage isn't above 25v or so after it was stored, the batteries are shot anyways.

If you have the Smart-UPS 1400 or 1500 TOWER type, then make sure your batteries are >20v

If you have the RACK MOUNT (1400RM2U) check the battery wiring and make sure EACH battery is registering above 10v for UPS to be even able to turn on and >12.4v if you expect batteries to have any usable capacity. So, if it's a 48v pack and you're reading 27v, then the batteries are beyond dead.

I

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

0 Likes
0
3049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:25 PM . Last Modified: ‎2024-03-15 04:08 AM

An RBC24 is made up of a paralled pair of 12 V 7.2 Ah cells in series, so it should be 26-27 volts.

Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore