Hi,
I use APC9619 card I am trying to get a decimal point from the environmental data. Via web for intance I can see 25.3C but via SNMP only 25. (I know it sais INTEGER). Is there a trick to get the decimal point as well?
Here is what I run and get on command line
$ snmpget -v1 -c public 10.0.0.33 SNMPv2-SMI::enterprises.318.1.1.10.2.3.2.1.4.1
SNMPv2-SMI::enterprises.318.1.1.10.2.3.2.1.4.1 = INTEGER: 25
$ snmpget -v1 -c public 10.0.0.33 SNMPv2-SMI::enterprises.318.1.1.10.2.3.2.1.6.1
SNMPv2-SMI::enterprises.318.1.1.10.2.3.2.1.6.1 = INTEGER: 30
Thanks
Ed
Attaching a screenshot with the web interface in the forground and terminal in front
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:28 AM . Last Modified: 2024-03-05 01:33 AM
Unfortunately, I don't see that this is possible for AP9619. The OID does not support tenths as you've found.
For AP9631, we do have an OID that is supposed to report this in tenths of a degree or percentage (for humidity) but it does not. I have a request in to address it for a future version though.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:28 AM . Last Modified: 2024-03-05 01:33 AM
I am not sure, But Like you said INTEGER, do you have option of FLOAT?
BR
Genjua
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:28 AM . Last Modified: 2024-03-05 01:33 AM
Unfortunately, I don't see that this is possible for AP9619. The OID does not support tenths as you've found.
For AP9631, we do have an OID that is supposed to report this in tenths of a degree or percentage (for humidity) but it does not. I have a request in to address it for a future version though.
Link copied. Please paste this link to share this article on your social media post.