Battery charge level drops quickly (Smart-UPS 750VA SMT750I) Calibration questions.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery charge level drops quickly (Smart-UPS 750VA SMT750I) Calibration questions.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Alex_N
Crewman Alex_N
Crewman

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:33 AM

0 Likes
7
3674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:33 AM

Battery charge level drops quickly (Smart-UPS 750VA SMT750I) Calibration questions.

I've bought a new UPS (APC Smart-UPS, 750VA/500W SMT750I) a month ago and it works fine but there's one thing that bothers me.

During the automatic self-test (that passes OK) the battery charge level drops to 90%. The self test lasts only a couple of seconds and I think a 10% drop is too much. The load on the UPS when the test is performed is about 21%. The runtime indicated by PowerChute Business Edition is 51 Minutes when the battery is fully charged and the load is 21%.

I'm thinking of doing a runtime calibration but I have some questions.

I've read here http://forums.apc.com/thread/15775 that "The calibration is just updating the battery runtime reported and if you don't have a problem with what's reported, no need for a calibration."

The runtime I've got seems OK (51 Minutes when not running on battery), my problem is with the battery charge level. Does the calibration also fixes this?

I've found here http://forums.apc.com/thread/8669?start=0&tstart=0 that "any UPS monitoring/shutdown software should be stopped from running in the background, and the serial cable should be detached from the UPS. This is necessary in order to prevent the software from shutting down the server/UPS due to an on-battery or low-battery condition. "

It's OK if I just disconnect the USB cable from the computer and start the calibration using the LCD display on the unit?

Thank you very much!


Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
3674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

You're very welcome.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Alex_N
Crewman Alex_N
Crewman

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:33 AM

0 Likes
0
3674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:33 AM

Experienced a power outage last weekend and I'm happy to say the UPS performed OK. smile After the initial 10% drop in battery charge it slowed down and after running on battery for about 4 or 5 minutes the charge level was only down to 87%.

I have one more question. I programmed the UPS using Powerchute Business Edition to shut down the computer after 4 minutes of running on battery and it did, but is there a way to put the computer in hibernation instead of shutting it down? I didn't find an option in Powerchute to hibernate instead of shutting down. I use Windows 7 and have hibernation enabled and working.


Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Alex_N
Crewman Alex_N
Crewman

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:33 AM

0 Likes
0
3674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:33 AM

I've bought a new UPS (APC Smart-UPS, 750VA/500W SMT750I) a month ago and it works fine but there's one thing that bothers me.

During the automatic self-test (that passes OK) the battery charge level drops to 90%. The self test lasts only a couple of seconds and I think a 10% drop is too much. The load on the UPS when the test is performed is about 21%. The runtime indicated by PowerChute Business Edition is 51 Minutes when the battery is fully charged and the load is 21%.

I'm thinking of doing a runtime calibration but I have some questions.

I've read here http://forums.apc.com/thread/15775 that "The calibration is just updating the battery runtime reported and if you don't have a problem with what's reported, no need for a calibration."

The runtime I've got seems OK (51 Minutes when not running on battery), my problem is with the battery charge level. Does the calibration also fixes this?

I've found here http://forums.apc.com/thread/8669?start=0&tstart=0 that "any UPS monitoring/shutdown software should be stopped from running in the background, and the serial cable should be detached from the UPS. This is necessary in order to prevent the software from shutting down the server/UPS due to an on-battery or low-battery condition. "

It's OK if I just disconnect the USB cable from the computer and start the calibration using the LCD display on the unit?

Thank you very much!


Reply

Link copied. Please paste this link to share this article on your social media post.

Alex_N
Crewman Alex_N
Crewman

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:33 AM

0 Likes
0
3674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:33 AM

OK, I think I'll postpone the calibration and see how it works during a real power outage. I don't want to stress the battery unnecessarily.

Thanks again for your help.


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
3674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

How many self tests have you done? The more you do, the more dramatic the drop will likely be. It is normal for the percentage to drop 5-8% at least I would say.

The runtime is a complex formula that is calculated from the state of charge (battery charge level) and the load on the UPS. The runtime is one of a couple of factors that affect the state of charge and can be potentially fixed with a run time calibration, but will not necessarily fix the drop of state of charge initial drop.

I've read here http://forums.apc.com/thread/15775 that "The calibration is just updating the battery runtime reported and if you don't have a problem with what's reported, no need for a calibration."

The runtime I've got seems OK (51 Minutes when not running on battery), my problem is with the battery charge level. Does the calibration also fixes this?

This comment is for a "manual calibration."

I honestly don't think a calibration is going to make a huge difference but if you'd prefer to try, then please note the following: If you do the calibration from the front panel command / test menu, you should not need to disconnect the communications cable. Since you are using PowerChute anyway, I recommend that you issue the command via PowerChute.

Please note this will discharge your battery down to between 10-20% and put additional stress on the batteries beyond the self tests you've already done. As I noted, a calibration will not necessarily "fix" the drop of charge you're seeing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Alex_N
Crewman Alex_N
Crewman

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
3674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

Thank you for your answer.

I've only initiated one self-test, the other where performed automatically by the UPS at 14 days since start-up date intervals. The self-test I've initiated was 2 or 3 days after the last self-test performed automatically to let the battery fully charge.

I also have an APC Back-UPS 800VA that I've used before the Smart-UPS 750VA and the battery charge level drop during the self-test was about 1-2%.


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
3674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

Hi again,

Oh, ok.

Well, to begin, comparing Back UPS and Smart UPS is like apples and oranges so I can't really say much beyond that.

I don't think there is much we'll be able to do unfortunately and it is just the way this particular model works but I can understand the concern with a larger drop like 10%. Upon checking though, it appears relatively normal.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
3675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

You're very welcome.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.