What configuration should be done on PowerChute Network Edition installed in a VMware environment (two ESXi powered by one UPS SURTD5000 XLI)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What configuration should be done on PowerChute Network Edition installed in a VMware environment (two ESXi powered by one UP...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
4
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

What configuration should be done on PowerChute Network Edition installed in a VMware environment (two ESXi powered by one UPS SURTD5000 XLI)

Hi,

What configuration should be done on PowerChute Network Edition installed in a VMware environment (two ESXi powered by one UPS  SURTD5000 XLI)

We installed Powerchute Network Edition following the installation manual and we configured the powerchute and UPS but after testing nothing happens, the VM's do not shutdown (attached the log files and screenshots of  UPS and powerchute configuration).Any suggestion please.

Regards

Adel

Attachments
Log Files.rar.zip
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

Hi,

As B wrote earlier, PCNS is reporting that it cannot communicate with 100.100.100.48 The log shows that PCNS never received any information from 100.100.100.48 that it was on battery. You need to resolve the communications issue before testing shutdown. We have Knowledge base document FA159624 that should help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

Hi,

What configuration should be done on PowerChute Network Edition installed in a VMware environment (two ESXi powered by one UPS  SURTD5000 XLI)

We installed Powerchute Network Edition following the installation manual and we configured the powerchute and UPS but after testing nothing happens, the VM's do not shutdown (attached the log files and screenshots of  UPS and powerchute configuration).Any suggestion please.

Regards

Adel

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

Hi Adel,

From the event logs I can see that there is a security mismatch error. The user name and authentication phrase need to match for PCNS to communicate with the NMC. The user name must be 3 to 10 characters and the authentication phrase needs to be 15 to 32 characters. If you verified they do match you can add the system IP addresses to the NMC PCNS client list manually to see if communications is established. If it does not then reset the NMC to the default settings, reboot the NMC, and change PCNS to use apc for the user name and admin user phrase for the authentication phrase.

If these steps do not help I will need to know what version of Java is installed on the systems, the model of the NMC, and the firmware version.

Can you also advise if these are standalone ESXi hosts or hosts that are part of a cluster and are being managed by vCenter?

If these are standalone hosts please get the build number of the PCNS you are using. This is under Help --> About.

Regards,

B

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

Hi,

The user name must be 3 to 10 characters (our account is apc CAD min 3 character)and the authentication phrase  must be 15-32 characters (our phrase is 'admin user phrase') So the user name and the sentence of authentication are correct.

The IP addresses are added. And solutions that exist is 2 ESX cluster managed by vCentre.

Vmware version is 5.1, the PCN is pcns310, Java version is jre-7u45-linux x64-and vesrion vmware appliance is vMA-5.1.0.1-1062361

Regards

Adel

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

0 Likes
0
1415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:28 AM . Last Modified: ‎2024-03-05 01:32 AM

Hi,

As B wrote earlier, PCNS is reporting that it cannot communicate with 100.100.100.48 The log shows that PCNS never received any information from 100.100.100.48 that it was on battery. You need to resolve the communications issue before testing shutdown. We have Knowledge base document FA159624 that should help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore