sua1500 power off button doesn't work

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • sua1500 power off button doesn't work
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

0 Likes
3
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

sua1500 power off button doesn't work

I have 4 sua1500 units and they all work, but one has a problem. 

The unit in question work perfectly with Power Chute Business Edition.  I have it connected to a PC and the test will work, it will calibrate, and shows 100% battery, and will do a timed shut down when losing power, and come back via the timer setting in Power Chute. The Power On (Test) button works perfectly, but the Power Off button will not shut the unit down when pressed.  As the unit works otherwise I don't think this is a showstopper as I rarely have need to manually shut it down.

Any suggestions as to why to Power Off button does not work?

Thanks in advance for any help and suggestions.

Rich Bendorf

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

I just checked the control board in the front panel of the SUA1500 and it has a dark coating (like solder flux) over the circuit board capacitive switch.  Also, the test switch, which works, does not have the coating.  Anybody know what I am talking about?  Any suggestions?

Thanks in advance for any help or insights.

Rich

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

Hi Rich,

Not sure what it could be besides the button no longer making contact or something is damaged, assuming the unit is several years old. There are a few different ways to turn the output of the UPS off thankfully - including via PowerChute (I think), the DB-9 serial port on the back of the UPS (between pins 7 and 9 of the DB9 for 200 ms (60Hz) 240ms (50Hz)), or via another accessory if you happen to add one at a later time (Network Mgmt Card, Dry Contacts Card, etc).

If you ever needed to "braindead" the UPS, which is typically done by holding down the button when AC power is removed, it automatically happens anyway after 8-10 minutes with no AC input power. Sometimes this is required for troubleshooting or resetting communications on any SUA model UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

Angela N....

Thanks for your reply.  I am a retired engineer and have worked in the computer/electronics field for many years...these UPS are a bit new to me, but I can figure them out. I have the APC serial cable and have access to the sua1500 via. the serial port.  I am primarily using PowerChute, which works fine.  I also have several AP9606 cards which I may install...so I should be able to control the unit that way.

Per your suggestion, The unit in question is probably 7 years old, don't remember the mfg. date, but works fine other than the power button.  I will try troubleshooting the power button and try bridging across switch contacts to see what happens... will let you know what happens.

Peace,

Rich Bendorf

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:00 AM . Last Modified: ‎2024-03-12 01:27 AM

I just checked the control board in the front panel of the SUA1500 and it has a dark coating (like solder flux) over the circuit board capacitive switch.  Also, the test switch, which works, does not have the coating.  Anybody know what I am talking about?  Any suggestions?

Thanks in advance for any help or insights.

Rich

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore