Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 03:12 AM . Last Modified: 2024-03-08 04:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:12 AM . Last Modified: 2024-03-08 04:50 AM
How can I manage my 60 ups's? I have net mg cards in them.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:12 AM . Last Modified: 2024-03-08 04:50 AM
if you want to manage the NMC's/UPSs, centrally, APC's tool is ISX Central -> http://www.apc.com/site/software/index.cfm/Products/?ID=350
it monitors the NMCs via SNMP and provides centralized management, alerting, mass upgrades and many other items. it also monitors third party devices via SNMP as I imagine you maybe have some non-APC devices.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:12 AM . Last Modified: 2024-03-08 04:50 AM
if you want to manage the NMC's/UPSs, centrally, APC's tool is ISX Central -> http://www.apc.com/site/software/index.cfm/Products/?ID=350
it monitors the NMCs via SNMP and provides centralized management, alerting, mass upgrades and many other items. it also monitors third party devices via SNMP as I imagine you maybe have some non-APC devices.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.